Dear all
Devoted couple of hours yestreday to save being reprimanded today
Results:
1. DHW running fine now, unscrewed pump screw and hot water cylinder union at top to bleed air.
2. All rads bled, CH working fine now as it should. Monster of a job really of reverse filling with mains water. The drain plug screw even when open a little leaks like hell, especially when mains is turned on full force.
3. I think I've found blockage, pic attached with area highlighted. I tried various settings on the motorised valve and with both the drain plugs but I am sure mains pressure was not reaching the area of blockage. Although
I find a little magnetic effect at some TEEs, magnet hangs on to the pipe at this Tee.
this tee looks like you cold feed
4. The system is running now as before with all rads incl new ones getting warm, BUT there is a blockage (not good as moogwai advised). FE tank water is like new (just replaced) and is not mixing with the CH one, so no point adding the cleaner or inhibitor.
If you could please look at the attached pic and advise how to clear this blockage? Could I undo the pump and poke the pipe as its quite close to the pump?
it needs to be cut out and repiped
What are the 2 valves on either side of pump? What are they for and how do you operate them?
theyre called pump valves, u screw the spindle clockwise to close the valve (beware, pump valves that havnt been used in yrs can start leaking when closed/opened,even more likely as youve defo got sludge in the system)
Regarding the gate valve on the cold outlet feed pipe on FE tank, I am not as educated as you on these things but I found that very useful to empty the FE tank and isolate the CH from FE tank. In fact I've another idea now,
should I try to mains flush the CH by opening the drain plug and connecting the CH feed at gate valve (undoing the gate valve) to mains pressure. Would that help to unblock the blockage?
most likely not, you'll most likely do some more damage elsewhere
it needs cutting out bud, i know its not what u want to hear but thats what needs done and trust me once its cut out the system will fill no problem.
Thanks once again.