Of the three recently fitted, two were in a system to our design and one was a customer free issue. In the later case, on the day, the Customer provided a much larger boiler than they originally proposed - so it could no longer be concealed within the kitchen fitments.
On one if the systems to our design, we made a mistake with the incoming flow rate. We measured it at 30lpm, but in hindsight we think that Thames Water were working on a repair and the flow was artificially high - in reality it is 20lpm, which is too low to deliver the blended hot water to two showers. We will fit a pumped accumulator in the New Year.
My experience of large domestic - 40kw plus boilers are that in general terms they need to within 20m of the incoming gas supply - with the majority of the gas pipework in 35mm and you need incoming flow rates of at least 30lpm - that is purely my view from getting an installation that delivers at low risk of non performance. My go to solution for non performing Combis is a pumped accumulator.
From the Customer perspective - the normal comments are - it is much noisier that my old boiler and it is a lot bigger than I expected.
I try to treat large Combi’s as I do air source heat pumps and take the Customer to see an operating installation first. For airsource around 50 percent decide against it on the grounds of noise.
I hope these comments help
From an installer perspective - if they cannot tell you on the first visit about supply suitability (gas) and routing, go elsewhere. Similarly on incoming flow rates, it needs to be above the boiler spec with a decent margin.
Please don’t read this as being against Combis. I am not, but from an installers perspective I don’t want disappointed customers