Boiler advice | Boilers | Page 2 | Plumbers Forums

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Discuss Boiler advice in the Boilers area at Plumbers Forums

Do you have the gas supply/meter to even feed a 50kw combi otherwise you're wasting your time considering one?
I’m looking at the 45kw Max now and would get it checked obviously prior to install.

What would be great is a video of two showers running off of the various boiler outputs with the correct pressures and flow rates so that consumers know what the reality actually looks like.
 
32kw heating and 34kw dhw. I have 18 rads so is this not a tad light on the heating side?

This is what I thought I was just getting. So is 34kw dhw going to run two showers satisfactorily? Or do I need the extra 10 kw for when that situation arises/
Attachment above says 32kw to heating and 29.3 to HW, it doesn't matter how efficient the boiler is, if its output to HW is 29.3kw then you can only get 12 LPM continuously from 5C to 40C. If its a storage boiler, then depending on the store size you can 16LPM or higher but for a limited period, I would like to see how they arrive at this 16 LPM number.

If you have these energy saving showers installed which limits the flow rate to 6 LPM, then, yes, just about possible to run two showers, I would measure the shower flow rate as is and you can then decide, also remember even if you can install a 50 kw boiler (gas supply etc, as pointed out) which gives 20.38 LPM, you will then have to restrict the showers to 10 LPM even if only one in service to allow both in use on the rare occasions you require them, so measure the present flowrate which will decide things, one way or the other.

CH output is probably OK especially if you have zoning.
 
I’m looking at the 45kw Max now and would get it checked obviously prior to install.

What would be great is a video of two showers running off of the various boiler outputs with the correct pressures and flow rates so that consumers know what the reality actually looks like.
The reality is exactly (IMHO) as I have shown for the various boiler outputs, it cannot be otherwise. If you ran 5 showers off this ( 29 kw) boiler then the flow rate will be restricted to 2.4 LPM, each, not very pleasant.
 
Last edited:
It is definitely impressive the flow rates large combis and storage ones offer.
My only consideration would be where do you go once they start to withdraw natural gas.(I appreciate that it may still be 10 yrs plus off.) Apparently other options produce considerably less energy and we may all have to look at stored hot water options and much more efficient homes. Just a thought, but may not be relevant on this decision.
 
Unless you had identical showers, flow and pressure in your home it would be pointless
What would be great is a video of two showers running off of the various boiler outputs with the correct pressures and flow rates so that consumers know what the reality actually looks like.

If you have limited space, budget or are happy To live with its limitations go for a combi.
If not - boiler and unvented cylinder.
 
Last edited:
Current Viessmans
It is definitely impressive the flow rates large combis and storage ones offer.
My only consideration would be where do you go once they start to withdraw natural gas.(I appreciate that it may still be 10 yrs plus off.) Apparently other options produce considerably less energy and we may all have to look at stored hot water options and much more efficient homes. Just a thought, but may not be relevant on this decision.
All Viessmann 200 & 300's are H2 ready or basically ready to run on a part hydrogen gas mix.

There's a 45kw Viessmann 200, it's semi commercial and almost double the cost of your WB 6000 at £3.5k but offers large flow rates.
 
I’m looking at the 45kw Max now and would get it checked obviously prior to install.

What would be great is a video of two showers running off of the various boiler outputs with the correct pressures and flow rates so that consumers know what the reality actually looks like.

Couldn't attach a file so here are a few numbers that may help you to choose your combi.

Continuous
Required
Recovery​
Power​
Mains​
HW​
Flow​
Stored Vol​
Flow​
Duration​
Time​
Output​
Temp​
Temp​
rate​
at 75C​
rate​
Period​
to 75C​
Kw​
DegC​
DegC​
LPM​
Litres​
LPM​
Mins​
Mins​
30​
5​
40​
12.3​
45​
16​
5.6​
3.7​
30​
10​
40​
14.3​
45​
16​
6.1​
3.7​
35​
5​
40​
14.3​
45​
18​
5.0​
3.1​
35​
10​
40​
16.7​
45​
18​
5.4​
3.1​
40​
5​
40​
16.4​
40​
10​
40​
19.1​
45​
5​
40​
18.4​
45​
10​
40​
21.5​
50​
5​
40​
20.5​
50​
10​
40​
23.9​
 
Last edited:
Over the last 2 months we have, at the customers request, installed 3 large ( 40kw plus ) combi boilers. Only one ( customer) is happy with the performance delivered.

I would add that none of the above are the WB 50kw offering, but only because the existing gas supply was not adequate
 
On this basis I hope you can see my conundrum. I have had 3 different boiler engineer come to my house and tell me 3 completely different things, which is why I am researching it myself.

So based on the likelihood of limited gas supply (yet to be determined) would you suggest a storage combi, if sticking to a no tank solution?

What were the customers not happy with? Flow rates?
 
If you haven't got the gas rate ie the energy to heat the water fast enough then you won't get the HW flow rate, any engineer who suggests just sticking in a high powered combi without a gas meter upgrade should basically be ignored.
 
If you haven't got the gas rate ie the energy to heat the water fast enough then you won't get the HW flow rate, any engineer who suggests just sticking in a high powered combi without a gas meter upgrade should basically be ignored.
Why would you need a gas meter upgrade? A standard meter provides 6m3/hr gas. Providing there’s no other appliances or just a small one such as a hob then no upgrade is required.

Obviously your pipe work has to be correctly sized, but I don’t see an issue and I’ve personally never had any issues in requiring the correct gas rate.

The issue would be more with your incoming water supply, on 15mm pipe work. If you’re wanting to require the correct flow rates you should be running a 22mm water main to the combi and 22mm off.
 
It's tight isn't it, yes a G4 has max capacity of 6m3 but really it's 4m3 with loss plus as you say you'd expect other appliances to be online simultaneously. Also you can't dismiss Bramble's experience with installing oversized boilers using a standard domestic meter. It doesn't seem that you get the real world performance you hope and pay for.
 
It doesn't seem that you get the real world performance you hope and pay for.
From my experience it isn’t that you haven’t got enough gas, it’s that the water pressure and pipe sizing which won’t give you the required flow rates to even get the figures they suggest.

For instance we’ve fitted a 35kw combi in a refurb, we’ve done a 22mm water main and 22 to outlets @ 2.5 bar it easily does 15lpm to 55oc. If that’d been 15mm pipe work I doubt we’ve be even getting 12.
 
Of the three recently fitted, two were in a system to our design and one was a customer free issue. In the later case, on the day, the Customer provided a much larger boiler than they originally proposed - so it could no longer be concealed within the kitchen fitments.

On one if the systems to our design, we made a mistake with the incoming flow rate. We measured it at 30lpm, but in hindsight we think that Thames Water were working on a repair and the flow was artificially high - in reality it is 20lpm, which is too low to deliver the blended hot water to two showers. We will fit a pumped accumulator in the New Year.

My experience of large domestic - 40kw plus boilers are that in general terms they need to within 20m of the incoming gas supply - with the majority of the gas pipework in 35mm and you need incoming flow rates of at least 30lpm - that is purely my view from getting an installation that delivers at low risk of non performance. My go to solution for non performing Combis is a pumped accumulator.

From the Customer perspective - the normal comments are - it is much noisier that my old boiler and it is a lot bigger than I expected.

I try to treat large Combi’s as I do air source heat pumps and take the Customer to see an operating installation first. For airsource around 50 percent decide against it on the grounds of noise.

I hope these comments help

From an installer perspective - if they cannot tell you on the first visit about supply suitability (gas) and routing, go elsewhere. Similarly on incoming flow rates, it needs to be above the boiler spec with a decent margin.

Please don’t read this as being against Combis. I am not, but from an installers perspective I don’t want disappointed customers
 
On this basis I hope you can see my conundrum. I have had 3 different boiler engineer come to my house and tell me 3 completely different things, which is why I am researching it myself.

So based on the likelihood of limited gas supply (yet to be determined) would you suggest a storage combi, if sticking to a no tank solution?

What were the customers not happy with? Flow rates?
One of the recommendations above is a Viessmann 111W. Based on what I read, this has a 45 liter storage tank and has a extra circ pump that circulates cold water through the heat exchanger and into the top of the cylinder so assuming this cylinder is heated to 60C then this boiler will (by my calcs) give the equivalent of a 160 liter conventional hot water cylinder at 60C so should supply 20 LPM at a deltaT of 35C for around 12 /13 minutes, before reheating required which should take around 5 minutes. Or, will supply 14.33 LPM continuously.
 
One of the recommendations above is a Viessmann 111W. Based on what I read, this has a 45 liter storage tank and has a extra circ pump that circulates cold water through the heat exchanger and into the top of the cylinder so assuming this cylinder is heated to 60C then this boiler will (by my calcs) give the equivalent of a 160 liter conventional hot water cylinder at 60C so should supply 20 LPM at a deltaT of 35C for around 12 /13 minutes, before reheating required which should take around 5 minutes. Or, will supply 14.33 LPM continuously.
Yeah it’s on my shortlist but the 8000 45 has a similar flow rate and is a much neater unit. Yes it will need more gas but assuming I have the required gas flow then I think the 8000 is probably my preferred choice.
 
Ok I have chosen my boiler. Thank you very much for all your help. It was much appreciated and one of the highest response levels I have ever had on any forum!

My next question is on radiators. All mine seem to get nice and hot with my current 35 year old potterton but I suspect most of them are the same age. Some will be newer from 2001 as there was an extension done around then but still old obviously.

Should they be changed as a matter of course at the same time?
 
That’s personal preference but you will have to change them later on depending on age can’t say how long they will last could do another 10 years might do 1 year if there functionally I would leave aslong as they heat the rooms
 
That’s personal preference but you will have to change them later on depending on age can’t say how long they will last could do another 10 years might do 1 year if there functionally I would leave aslong as they heat the rooms
I would probably prefer to do them at a different time from the boiler. Maybe in the summer so that I don’t have a double whammy with the cost. A good flush and a filter installed should protect the new boiler I guess.
 
Probably obvious but do combi boilers modulate on the hot water side as well as the heating. Presumably they don't use all of their "power" all of the time on that side either, if only a tap is lightly turned on?
 
Yes, AFAIK they do but normally a flow switch on the DHW side is arranged to to cut out the boiler or something like that corresponding to the minimum turn down of the boiler, the reason being I presume to prevent the HW running hot and cold with a very low flow demand and possibly for boiler Hx protection as well.
 
Ok. So I have had my 8000 45 combi installed and there has been no issue with either the gas supply or the water flow as both exceed requirements where I am. My showers are transformed into amazing power showers, really cannot believe the difference, so the hot water side is flawless.

On the heating side, I have a query for anyone that has specific 8000 experience...my heating side is set to 75 degrees and it seems to build up to it in stages. So the house was freezing after the install down in single digits centigrade. My expectation was that the boiler would heat up to 75c on heating side and hold it there until the thermostat in my hallway cut it off at the desired temp. However it seems to heat up to 50 odd, then 60odd and I have seen it go into the 70s once (not standing looking at it all day). The plume stops in between so it is going off...should it do that?

The radiators seem to get hot and then cool and then hot again, rather than it just remaining even. As the day is going on, it might be getting better but not sure yet so thought I would ask if any of this make sense?
 
Your expectations should be met.
Looks as if the boiler is cycling, can you open up all your rads, zone valves, TRVs, whatever fully, and see the boiler reaction, also can you see what the minimum output is on CH,. Even though you shoiuldn't have to do it IMO, you may be able to range rate the boiler on CH to 25kw or whatever the total rad output is, what does your installer say?.
 

Similar plumbing topics

S
Morning all, I have a Worcester Bosch 8000...
Replies
0
Views
694
Simon from Watford
S
M
A large storage combi could feed more than two...
Replies
5
Views
910
The Orion is about 65% efficient so not great...
Replies
10
Views
3K
M
I have a viessman vitodens 222F combi storage...
Replies
0
Views
591
Max Hill
M
You will need a check valve to stop reverse...
2 3
Replies
61
Views
7K
Back
Top