Even though I am reasonably happy that a fan speed of 1500 RPM is min output of ~ 5.2kw, this is not borne out by using the flowrate of 1M3/hr and a deltaT of 9C which gives a output of 10.46kw, if the deltaT is correct then the actual flowrate is only 0.5 m3/hr for a output of 5.2kw, if the flowrate is correct then the deltaT is only 4.5C. Would like to monitor the gas meter.
Condensing: Achieving the utopia of 100% condensing requires a flue gas temperature of down around 30C which requires a return water temp still lower of ~ 20/25C, so you will always see a plume from the boiler unless these conditions are met, IMO to achieve ~ 3/4% condensing benefit requires a return temp of ~ 45C, the big advantage of condensing vs non condensing is that even when not condensing there is a big benefit, a non condensing boiler might have a flue gas temp of 230C (like my own) but a condensing boiler will easily achieve ~ 80C (non condensing) with a gain of ~ 7%,
I would definitely try and run on the return target temp of say 40/45C, you can then adjust flow rates etc to give optimum comfort and performance.