Looks like there is a 60 minute time out to do editing, which is a pity.
UPDATE
1- I have set the boiler to 18KW, first time ever....its modulating ok, but have had to reduce the target temperature to 68oC to keep the inlet below 55oC.....so quite a low DT
2-occasionally the pump declares ‘LO FLOW’ then shortly after shuts off, restarts with the same message, then after a few minutes reverts to the previous readings I.e. 0.7m3/Hr etc....set it to heating only for now to establish that works ok.
not sure if the higher flow; which it looks like I have, has dislodged some debris and causing the pump problems.....or it’s something else, all rads now very hot, even one in a room which previously struggled to get warm. Ideally want to heat the hot water in the day, together with the heating, as on hot water only, I don’t think I will get a low enough inlet temperature for condensing.... going to try again tomorrow....also if I try to heat the hot water on its own, not sure if the DT between the immersion cylinder and boiler outlet is enough
thanks for the replies......very confused about the pump setting options., is CP3 the middle icon of the three ..?.....happy to have a lower flow if it helps the DT....will look at the charts again...
still worried about the LOW FLOW message, although hasn’t happened since a few hours ago....🤞
also was considering increasing two lounge rads from single to double, won’t increase the flow obviously bit will emit extra heat and help the boiler DT, any thoughts ?
UPDATE
1- I have set the boiler to 18KW, first time ever....its modulating ok, but have had to reduce the target temperature to 68oC to keep the inlet below 55oC.....so quite a low DT
2-occasionally the pump declares ‘LO FLOW’ then shortly after shuts off, restarts with the same message, then after a few minutes reverts to the previous readings I.e. 0.7m3/Hr etc....set it to heating only for now to establish that works ok.
not sure if the higher flow; which it looks like I have, has dislodged some debris and causing the pump problems.....or it’s something else, all rads now very hot, even one in a room which previously struggled to get warm. Ideally want to heat the hot water in the day, together with the heating, as on hot water only, I don’t think I will get a low enough inlet temperature for condensing.... going to try again tomorrow....also if I try to heat the hot water on its own, not sure if the DT between the immersion cylinder and boiler outlet is enough
thanks for the replies......very confused about the pump setting options., is CP3 the middle icon of the three ..?.....happy to have a lower flow if it helps the DT....will look at the charts again...
still worried about the LOW FLOW message, although hasn’t happened since a few hours ago....🤞
also was considering increasing two lounge rads from single to double, won’t increase the flow obviously bit will emit extra heat and help the boiler DT, any thoughts ?