You mentioned increasing the rad sizes so I came up with the following numbers based on that., I based them on doubling the rad outputs but can calculate it for any increase you want.
Based on your actual results it seems that you have a a relatively small installation with total rad output of ~ 9 kw.
If you look at the 9kw base below (top row) you can see that your actual output is 6.73kw with a return of 52C. If you were to increase (second row) the flow rate (CP2/CP3) to 0.63M3/hr to keep the boiler happy then by reducing the flow temp to 60C you will still get a return of 52C BUT a reduced output of 5.87kw, you would againthen need to up the flow temp on HW.
If you now doubled the rad outputs to 18kw, again with a happy boiler flowrate of ~ 0.6M3/hr, you can see the effect of different flow temps on rad output etc, if you select a flow temp of 60C then you will get a return of 44C and a output of 10kw, you would need to up the flow temp on HW.
If you select a flow temp of 72C then you will get a return of 52C and 14.35kw output and so on.
Table Below might be of some help.
| | | Flow | Return | DeltaT | Boiler | Boiler | Boiler |
| | | Temp | Temp | Temp | Output | FlowRate | FlowRate |
| Deg rad | Output | Deg.C | Deg.C | Deg.C | KW | LPM | M3/hr |
9KW Base | 40 | 75% | 68 | 52 | 16 | 6.73 | 6.03 | 0.36 |
| 36 | 65% | 60 | 52 | 8 | 5.87 | 10.52 | 0.63 |
| | | | | | | | |
18KW Base | 32 | 56% | 60 | 44 | 16 | 10.08 | 9.03 | 0.54 |
| 38 | 70% | 68 | 48 | 20 | 12.60 | 9.03 | 0.54 |
| 42 | 80% | 72 | 52 | 20 | 14.35 | 10.28 | 0.62 |