Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.
Discuss Classify this please doubting myself in the Plumbing Jobs | The Job-board area at Plumbers Forums
I said the terminology doesn't officially exist so when dealing with unsafe situations you cannot use NCSNCS DOES still exist. You just cannot use it on warning notice. This is basic stuff that has been discussed extensively.
If the hole was 30mm higher/ further away, it would not even be NCS.
A challenge: show me where in the Unsafe Procedure this is AR.
I said the terminology doesn't officially exist so when dealing with unsafe situations you cannot use NCS
And following this chart, I would class the install as AR
View attachment 37674
The other problem with NCS is for a newly qualified engineer such as myself. We aren't taught about it. All we are told is it no longer exists and the only terms we now have are AR and ID.
..but the flue still falls outside of the minimum requirements. And they are requirements, not recommendations. So when you follow the chart "does a situation exist which may lead to an unsafe situation". In my eyes yes it does. An extremely windy day, could blow POC's back into the opening. So the appliance is at risk and should be turned off until rectified. After all, I don't want to be the "other guy" .
And regarding NCS, in my training, we was told that instead of NCS we now have 2 categories of AR, 1. Where turning the appliance off would remove the risk and 2. Where turning the appliance off wouldn't remove the risk.
From what I can gather, it's to make the warning system clearer for the client. Label something as NCS and the client will take no action, label it as AR and the client will be more likely to act. So as far as I'm aware, when an appliance is non compliant, we fill out a warning notice but we don't attach a label and we don't turn the appliance off.
Found this that will clear up this NCS stuff. Long red box on the side.
UnsafeSituations-1.pdf
I would class this as NCS as if it was AR it would mention in in the GIUSP, only mention is if POC are entering then it is ID.
But if it has no terminal guard and is within 300mm of the boundary to next door then it could be argued to be AR but still not a 100% AR.
@Riley what boiler is it?NCS DOES still exist. You just cannot use it on warning notice. This is basic stuff that has been discussed extensively.
If the hole was 30mm higher/ further away, it would not even be NCS.
A challenge: show me where in the Unsafe Procedure this is AR.
All FFs are 300mm, if that is why you are asking?@Riley what boiler is it?
No I was not around with the old system. Worked on gas installs but that was it. My training was all based round the new system but even that was vague. I haven't seen the old unsafe book, haven't seen the new one either, I really should order one.TBH, you have slightly confused the 2 types of AR issue. There are a couple of instances where this applies, one of which is a built over service. You issue a Notice, but not a Label. There are one or 2 similar ones, but cant think of them right now. It has nothing to do with NCS.
The new system WAS brought in to try to avoid confusion. I assume you were not around with the old? We had a DO NOT USE label, which was only used on ID - IIRC, there was no AR label, just a notice, but I am honestly not sure. Either way, both AR and ID are now labelled more emphatically.
NCS was removed from the UP as it felt it was confusing and diluted the message. (I am not convinced, but that is another debate). You can still write down NCS but NOT on a warning notice.
Re non compliance = automaticaly AR: Absolutely not.
You have presumably not had the advantage of seeing the old Unsafe Procedure Book, which listed many more scenarios, which were indicated as NCS. The scenario in question would have been in the old book. If I can find an old one, I will copy and post.
For example, a cooker point should be 750mm above the floor. Would you AR it if it was 650mm? The 750mm is a REQUIREMENT as well. There are countless examples.
Without looking it up, do you remember, if specifically told, or work out, what the classification is for an ECV that is passing gas when OFF?.
On an extremely windy day, the POCs will be massively dispersed and diluted. No way will they enter through the grid on the old terminal (I assume you do know what the outer wall part of that terminal in the picture is like?)
Just noticed your last comment:
So as far as I'm aware, when an appliance is non compliant, we fill out a warning notice but we don't attach a label and we don't turn the appliance off.
That is wrong. With the exception of the couple I mentioned earlier, every Notice is accompanied by a Label. You DO NOT use a WL for anything other than a declared AR or ID.
Incidentally, how would you "turn off" an AR appliance?
Regarding ncs, wasn't that for old installs that don't meet current regs? Not a get out clause for poor new installs.
The terminal I can't tell you what it looks like. I also can't see how it matters, you can see clear daylight through it with not much restricting it.
The cooker hose I don't know, again you can't install to NCS so what does an engineer do who spots it? I would say it depends if the hose is touching the floor or not.
No I was not around with the old system.. My training was all based round the new system but even that was vague. I haven't seen the old unsafe book, haven't seen the new one either, I really should order one.
.
You are absolutely correct, one must work to the standards, and if a customer were to have gas Safe inspect a job, everything not correct would be subject to demand that you alter it. But, if a GS inspector were to spot a vent too close to a boiler, or a cooker point in the incorrect position, he still would not apply the AR procedure - because those situations are classed as NCS.
So, faults that you come accross have to be assessed for safety, and you must decide in which category it falls. Even of the job is 2 weeks old, it is existing. Not every fault is classed as at risk, but things like fumes are not as black and white as, say, a cooker point. I suppose my main ssue with this situation is "why would you leave it, if you fee l is AR". If you apply AR properly, the appliance is only turned off at the customer control, the customer then decides whether to use it or not. It is often quicker to sort out problems than complete the paperwork, explain to the punter and field all the arguments.
If an RGI spotted the cooker hose, he would either note it as NCS or ignore it. Or, obvioulsly, quote to rectify. You cannot INSIST that the work is done, and it would be wrong to do it, charge and tell the customer that youwere required to do it. You cannot invoke an AR procedure because it "looks wrong", to CYA, or "to err on the side if safety". You wll struggle to get paid for the paperwork etc, whereas you can legitimately charge for the rectification - provided you have set up your systems properly. In this case, TBF, it may have been more awkward as the terminal is in the neighbours garden.
Inshort, you have the concept and prctice of the Unsafe procedure slightly muddled. I am not trying to have a go at you, you are not unique and one has to gain experience. Unfortunately, there are a lot of experienced guys who get it wrong, expecially on this forum - but be careful not to follow the herd.
You say you have not got the book? You don't really need it, as it is all online. (I assume you have seeen the online version?) If you do not carry a tablet, then it is worth buying the printed version, even if it is to be able to show an argumentative customer.
One thing I can’t seem to comprehend, we are working to the latest version of GIUSP, which doesn’t give clear guidance on this particular issue from what I can see. Therefore how could you possibly know that previously it was ID or ncs, you couldn’t unless you sought advice from gas safe/this forum? Therefore I can’t see doing wrong what you as an engineer think is the right thing?
Sparked a long and healthy debate there @Riley
It doesn’t actually remove the risk, if they turn it back on againI agree, with the others AR, and turned off (as it removes the risk). It terminates into neighbours garden? I’d be looking at advising a plume management kit also. Recommended to remove that old flue and brick up/fill with suitable,material.
Thank you for your time and detailed replies, I'm still confused at the whole ncs thing, but that's down to training and to be fair, in my current role I don't come across that many unsafe situations, haven't even wrote a warning notice out.You are absolutely correct, one must work to the standards, and if a customer were to have gas Safe inspect a job, everything not correct would be subject to demand that you alter it. But, if a GS inspector were to spot a vent too close to a boiler, or a cooker point in the incorrect position, he still would not apply the AR procedure - because those situations are classed as NCS.
So, faults that you come accross have to be assessed for safety, and you must decide in which category it falls. Even of the job is 2 weeks old, it is existing. Not every fault is classed as at risk, but things like fumes are not as black and white as, say, a cooker point. I suppose my main ssue with this situation is "why would you leave it, if you fee l is AR". If you apply AR properly, the appliance is only turned off at the customer control, the customer then decides whether to use it or not. It is often quicker to sort out problems than complete the paperwork, explain to the punter and field all the arguments.
If an RGI spotted the cooker hose, he would either note it as NCS or ignore it. Or, obvioulsly, quote to rectify. You cannot INSIST that the work is done, and it would be wrong to do it, charge and tell the customer that youwere required to do it. You cannot invoke an AR procedure because it "looks wrong", to CYA, or "to err on the side if safety". You will struggle to get paid for the paperwork etc, whereas you can legitimately charge for the rectification - provided you have set up your systems properly. In this case, TBF, it may have been more awkward as the terminal is in the neighbours garden.
In short, you have the concept and practice of the Unsafe procedure slightly muddled. I am not trying to have a go at you, you are not unique and one has to gain experience. Unfortunately, there are a lot of experienced guys who get it wrong, especially on this forum - but be careful not to follow the herd.
You say you have not got the book? You don't really need it, as it is all online. (I assume you have seeen the online version?) If you do not carry a tablet, then it is worth buying the printed version, even if it is to be able to show an argumentative customer.
It doesn’t actually remove the risk, if they turn it back on again
Wow, you really know how to lower someone’s self esteem - I bow to your superior knowledge. I thought joining this forum would make me a better engineer, but all it’s done is make me question my ability as an engineer. However I must thank you for making me realise that sooner rather than later. I can now look to be either doing something else or carry on with my mediocre work and life.
I’ve lost face, ive lost faith in the gas industry and some of the training methods used, and lost faith in myself. I hope you can impart your superior wisdom and knowledge to someone who isn’t afraid of his own shadow.