Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Condensing bolier flow and return temps - effect on rad sizing? in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.
My opinions:

28i Juniors aren't very good. I'd recommend going for a Worcester CDi (if you want Worcester) unless it is a flat/rental property. Personally in that price range a Vaillant Pro 28 installed by a Vaillant Advance installer (5 year warranty instead of 2) is a much better buy.

Unless you live in a very large property I wouldn't worry to much about F+R temps. You can size the radiators yourself by googling 'radiator sizing' and measuring your rooms.

Worcester Accredited means absolutely precisely nothing. Just means he installs a fair few boilers. It is no indication of quality, and in most cases you are paying for that extra warranty indirectly. Just so you know.

i would not fit a vaillant myself, we all have our own ideas what makes a good boiler and manufacturer.

what makes a vaillant advanced installer better than a worcester accredited installer out of interest?
 
As for rad sizing, you can do this yourself on the internet at loads of places, if you want to do it long hand get a book and have a go. If your old rads have no convectors/fins then a new rads of the same size will give more ouput if your were comparing apples to apples (with fins:)).

Your the customer at the end of the day, you can take the advise of your engineer but if you want a larger rad as your the person paying and lives in the property then that what you should have. You can make it as complicated or as simple as you want, your paying you have what you want.
 
what makes a vaillant advanced installer better than a worcester accredited installer out of interest?
Didn't say it was 'better'. WA installers give longer warranties, which in many cases they (aka you) are paying for. VA installers can give longer warranties for free.
 
Didn't say it was 'better'. WA installers give longer warranties, which in many cases they (aka you) are paying for. VA installers can give longer warranties for free.


yes but they steal your service work...
 
Just to throw something else into the mix Rory about your boiler selection & controls, are you aware of Weather Compensation a few of the boiler manufacturers have this already built into the electronics so with a low cost thermistor kit it can be activated.

I would recommend this as it will work nicely with your new system, it basically varies the water temp to suit the outside temp thus keeping the boiler in condensing mode for longer periods without effecting the comfort levels. (why is it in there? cos in a most of europe it has to be installed & working).

Can I say, it would be nice to have a more customers who took such an interest in there heating systems, as it might start to raise the standards of design in the domestic industry let along the installation quality.
 
Last edited:
I work my room heat losses out @ delta 50 1 degree = 2% i up size by 20% which gives me a delta 40 heat figure for each room.
Assuming that delta X is the difference between room temperature and the mean rad temp [(flow+return)/2], then unfortunately a 20% drop in the delta does not give a 20% drop in the rad output; it's nearer to 25%.


I set flow temp to 65 allowing room temp to be 15...... Delta 40!
That assumes the return is 45.

But what if the customer doesn't want his house at 15? Answer: your rads will be undersized by 20%.

Output of a "1 kW" rad at different temps:

75/65/15 = 1.14 kW
75/65/20 = 1.00 kW
65/45/15 = 0.73 kW
65/45/20 = 0.60 kW
 
Assuming that delta X is the difference between room temperature and the mean rad temp [(flow+return)/2], then unfortunately a 20% drop in the delta does not give a 20% drop in the rad output; it's nearer to 25%.



That assumes the return is 45.

But what if the customer doesn't want his house at 15? Answer: your rads will be undersized by 20%.

Output of a "1 kW" rad at different temps:

75/65/15 = 1.14 kW
75/65/20 = 1.00 kW
65/45/15 = 0.73 kW
65/45/20 = 0.60 kW
Modern design recommendations on design room temps Rad's = 21deg C U/F = 20deg C
I use 21 (for rads) in all rooms, easer that way.
 
As Chris has mentioned wether comp, IMO it's an absolute must , the sensor for my boiler at home was approx £100 (viessman 200) it's nicked plenty off my gas bill, the big thing if you go for it your house must be WELL insulated.
To use it you strangely have to rethink the way your heating system works, ie her indoors constantly telling me the rads aren't hot, my reply , are you warm , answer yes, is the house warm , answer yes, = low gas bill .
 
Assuming that delta X is the difference between room temperature and the mean rad temp [(flow+return)/2], then unfortunately a 20% drop in the delta does not give a 20% drop in the rad output; it's nearer to 25%.



That assumes the return is 45.

But what if the customer doesn't want his house at 15? Answer: your rads will be undersized by 20%.

Output of a "1 kW" rad at different temps:

75/65/15 = 1.14 kW
75/65/20 = 1.00 kW
65/45/15 = 0.73 kW
65/45/20 = 0.60 kW

15 is the starting room temperature allowing up to 25 which would give a room to rad difference of 40
 
15 is the starting room temperature allowing up to 25 which would give a room to rad difference of 40
Sorry, but I don't follow what you are saying.

The accepted method is to calculate the heat required to raise the room temperature from -1C (or -3C) to 21C. I don't see where 15C or 25C fits in to that.
 
I have weather compensation in my own house and fitted it for a few people. It is great but requires a lot of time and effort to get set up correctly. It took me a full winter and and a wee bit of the next to get my whole house perfect.
Its a big undertaking to play with the heat curve, balance the rads perfectly and get room temps correct.

By the way, all I mean about paying a bit more is the people who know their stuff generally charge a bit more than *** packet man.
 
Sorry, but I don't follow what you are saying.

The accepted method is to calculate the heat required to raise the room temperature from -1C (or -3C) to 21C. I don't see where 15C or 25C fits in to that.

What I'm saying is who let's there room get to -1 if the heating is set to have a minimum fall back temp of 15 the rads will be over sized not 20% under like you said.
 
What I'm saying is who let's there room get to -1 if the heating is set to have a minimum fall back temp of 15 the rads will be over sized not 20% under like you said.
An interesting approach! But how do you heat the house up from cold if it has been empty for a few weeks and the heating has not been left on?

Can you assume that the heating will not be allowed to drop below 15C?
 
Just to throw something else into the mix Rory about your boiler selection & controls, are you aware of Weather Compensation a few of the boiler manufacturers have this already built into the electronics so with a low cost thermistor kit it can be activated.

I had originally thought I'd get a Nest learning thermostat, but the installer has suggested Worcester's Wave. Allegedly it does both weather compensation (getting the temp from a local weather station) and optimisation.

I must admit that (like much of this stuff!) I'm bemused by how these things optimise - surely these remote units (which seem to basically just be fancy thermostats) can't control the boiler flow temp?
 
Because most of my customers ask me to set there heating up for them. I have an off temp of 15 to keep some comfort and avoid large heat up periods. I would hope the boiler doesn't get turned off as there would be no frost protection! If it was off for a while tho it will heat up fine may take a little longer but will be condensing all the way. To be honest I oversize slightly on my calcs anyway and never had a problem.
 
I had originally thought I'd get a Nest learning thermostat, but the installer has suggested Worcester's Wave. Allegedly it does both weather compensation (getting the temp from a local weather station) and optimisation.

I must admit that (like much of this stuff!) I'm bemused by how these things optimise - surely these remote units (which seem to basically just be fancy thermostats) can't control the boiler flow temp?
As far as I am aware they are as you say Rory " fancy thermostats" i.e. optimal start / stop & yes the full on W/C controllers can be both expensive & a bit complicated to set up with the right curve to suit your older less insulated house but you may well enjoy the challenge in the knowledge that it is saving you money.

I have the simplest form my Viessmann Vitodens 100-W (heat only) had it built-in as I say, it cost me about £20 for the out side kit + some 1.5mm 3 core flex. I had to alter the controls wiring to suit my existing S plan but you would have a diverter valve 3 port installed with the new system.

I can adjust the compensate curve on mine by altering the position of the boiler thermostat knob, about 2 or 3 times during the last two heating seasons I have had to turn it up (when it was very cold) the rest of the time it looks after its self.
For this amount of outlay & time spent why would you not take advantage of this? Don't over complicate.
 
Nest, Wave, hive and Tado are all fancy on off switches. None of them control flow temp. Proper weather comp does.
 
OK, so our standard retrofit for renewables, (heatpumps and biomass) includes Honeywell Evo throughout AND weather compensation, - Yes our customers are of the more discerning type, (only worked on two semis in 4 years) and they are all over the moon with their finished systems - customer satisfaction rating in the 5 stars bracket.

The Evo controls room by room temps by time of day with room by room override, and the weather compensation controls the flow temperature, so maximising the efficiency of the heat pumps and biomass boilers - especially important as these are not on/off devices like gas and oil boilers.

You'll have trouble beating the simplicity and sophistication of the Honeywell Evo system.

Going back to my earlier post on heating design - for the power output - boiler and rad sizing you add in factors to cover wether you heat from cold and weather the system is run continuously or intermittently (i.e on day off at night, or set back) - Also standard room temperature designs are 21,22 and 18 dependant upon use. - your radiator size is therefore affected by output (kW) required, flow temperature and room temperature.
 
Nest, Wave, hive and Tado are all fancy on off switches. None of them control flow temp. Proper weather comp does.

Worcester say the Wave does control the flow temp (from the installion instruction):

"The Wave uses Load Compensation as standard to
continuously monitor and control the room temperature during
your programmed central heating times. This function offers
energy savings compared to standard on/off controls.
The compensation feature means that, rather than just
switching the boiler on and off, it will adjust the flow
temperature of the central heating water in line with your
central heating set temperature. The smaller the difference
between the actual temperature and the set-point
temperature, the lower the flow temperature from the boiler."



The only thing I'm a bit miffed about now is that we are stuck with 28i Junior - I asked for 29CDi Classic but apparently it's not instantly available as it's not a popular choice at that size (people usually for got the Junior or Compact). Anyway, the Classic has only just been updated so chances are I might have got an "old" one, and then I'd be annoyed about that!
 
Last edited:
I would hope the boiler doesn't get turned off as there would be no frost protection!
That' a big hope. What happens when the house gets sold, the old owners move out but the new ones' don't move in for a couple of weeks? The insurers could insist that the heating gets turned off and everything drained down. So the new owners move into a cold house.

If it was off for a while tho it will heat up fine may take a little longer but will be condensing all the way. To be honest I oversize slightly on my calcs anyway and never had a problem.
If you have designed for a temp rise of 10C, it doesn't matter if it's 10 degrees from 0C to 10C, or from 15C to 25C. You will still need the same amount of heat. If you want to raise the temp by 20C you will need double the amount of heat. It will take more than "a little longer" to achieve that.

I would be really interested to see a sample of your calculations.
 
That' a big hope. What happens when the house gets sold, the old owners move out but the new ones' don't move in for a couple of weeks? The insurers could insist that the heating gets turned off and everything drained down. So the new owners move into a cold house.

As a customer, I have to say I would be pretty dismayed if an installation was sized based on such a rare occurance.
 
As a customer, I have to say I would be pretty dismayed if an installation was sized based on such a rare occurrence.
That particular scenario might be rare, but it's no different from a new-build house, which has to be heated from cold when the first owners move in, which could be in the winter when the house, and outside temperature, are below freezing.

A system which has been designed to raise the temperature 10C will never be able to raise it 20C.
 
That particular scenario might be rare, but it's no different from a new-build house, which has to be heated from cold when the first owners move in, which could be in the winter when the house, and outside temperature, are below freezing.

A system which has been designed to raise the temperature 10C will never be able to raise it 20C.
But you just wait for a time or day when the outside air temperature is not -3 (or what ever it has been designed to) you will then have to less heat going out & the emitter will raise the room air temp or you could turn the boiler stat up to increase the water temp & therefore the output, before resetting.

What I would suggest you don't do is design your system for these one off or very rare occasions as this will effect the day to day efficiency's.
 
But you just wait for a time or day when the outside air temperature is not -3 (or what ever it has been designed to) you will then have to less heat going out & the emitter will raise the room air temp or you could turn the boiler stat up to increase the water temp & therefore the output, before resetting.
I can just imagine the conversation between the proud owner of a brand new £350K house and the site's sales rep when he is advised not to move in to the house as the heating system is not powerful enough to bring the house up to an acceptable temperature.

As for the second suggestion, is that always possible? Turning up the water temperature will increase the rad output, but you will still be limited by the boiler output. If you need 10kW for a 10C rise, you will need 20kW for a 20C rise. Who installs a boiler with 50% spare capacity?

What I would suggest you don't do is design your system for these one off or very rare occasions as this will effect the day to day efficiency's.
But isn't that how systems are supposed to be designed, i.e. for an outside temp of -3C?
 
Last edited:
Status
Not open for further replies.

Similar plumbing topics

You've already spent thousands on a new boiler...
Replies
2
Views
954
Thanks guys. Just finished and managed to set...
Replies
9
Views
2K
  • Question
'Have tried all off bar A, B, and C, so not...
Replies
3
Views
812
R
  • Locked
Hey all, apologies for the long post: I've...
Replies
0
Views
4K
richardc1983
R
J
  • Locked
Yep u want as few variables as possible...
Replies
24
Views
9K
Ermintrude
E
Back
Top