i remember when we cubed the room in ft and times by 5 to get the rad size then choose the rad that fitted the window
Last edited:
Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws
Discuss Condensing bolier flow and return temps - effect on rad sizing? in the Plumbing Jobs | The Job-board area at Plumbers Forums
I think some installers still use that method.i remember when we cubed the room in ft and times by 5 to get the rad size then choose the rad that fitted the window
If you do that and compare it to results from a mears calculator its always there or thereabouts [emoji89]i remember when we cubed the room in ft and times by 5 to get the rad size then choose the rad that fitted the window
Ok so hear goes I work my room heat losses out @ delta 50 1 degree = 2% i up size by 20% which gives me a delta 40 heat figure for each room. I then work out the system requirement and add 10% for pipework heat loss. I range rate the boiler through the perameters at a Max of this figure. I set flow temp to 65 allowing room temp to be 15...... Delta 40! Completely balance the system for equal heat loss per rad and fit an external weather compensator. Fit a fully modulating boiler with adjusting pump speed and system learning capabilities and there you have it the most condensing system you can get. This will cost you mind and most are not willing to pay for this level of service!
I applied that formula to my living and dining rooms; and got the following results:i remember when we cubed the room in ft and times by 5 to get the rad size then choose the rad that fitted the window
That's the one quirky thing that gets me, not just on here, but youtube videos as well.
You state 10% heat loss for pipework; and here's the thing: a massive percentage of the pictures we see on here and youtube, the installers never bother to insulate the pipework.
P.S. And as someone who still has his WB GREENSTAR 28i j ( Which magazines best buy) still in its box. This thread is a tad painful:-(
I can just imagine the conversation between the proud owner of a brand new £350K house and the site's sales rep when he is advised not to move in to the house as the heating system is not powerful enough to bring the house up to an acceptable temperature.
As for the second suggestion, is that always possible? Turning up the water temperature will increase the rad output, but you will still be limited by the boiler output. If you need 10kW for a 10C rise, you will need 20kW for a 20C rise. Who installs a boiler with 50% spare capacity?
But isn't that how systems are supposed to be designed, i.e. for an outside temp of -3C?
I just use the 10% as a rule of thumb but it is surprising how much heat can be lost through pipework. Why do you say quirky?
What are the flow and return temperatures?As 'promised' by the installer, flow and return seemed very similar temperatures.
What are the flow and return temperatures?
That doesn't sound right. There should be a noticeable difference between the flow and return - about 20C - despite what the installer told you. If you can, borrow an infrared thermometer and measure the flow and return pipes near the boiler. Do the same for a few of the radiators. As the pipes are all brand new and probably unpainted, you will need to wrap some insulating tape round the pipe and measure the temperature off the tape, holding the thermometer almost in contact with the pipe.I can't say with any precision at the moment, but by touch both very hot with little difference between them.
That doesn't sound right.
Try opening the rad valves more to help the system give up more heat and turn the boiler temp down (sorry can't remember boiler type and too lazy to read back haha)
And you would be right Rory.Oh - that's the opposite of what I'd have thought. My instinct would be to close them down to slow the flow. Worcester 28i Junior, by the way.
OP did you have to set up your heat curve using the app?