Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Do I need a new boiler? in the Boilers area at Plumbers Forums

Status
Not open for further replies.
P

pch

Boiler is 5 year old Potterton Performa 24 Eco HE, has worked perfectly till now supplying hot water & 9 rads. Have previously had to refill & bleed rads only very occasionally.
Last few weeks had to refill more frequently till would not keep pressure for even a day, then noticed drips from boiler and switched all off & called engineer.
He diagnosed possible leak at/in heat exchanger & faulty diaphram in 3 way valve.
Due to cost of heat exchanger he first replaced O rings/seals in feed pipe & reassembled & tested, however now said system was leaking from several places including secondary heat exchanger, and would be much quicker & better long term value to replace boiler with latest version Potterton 25 Eco HE.
I got impression that he did not know what was causing all the leaks & did not wish to keep diamantling & changing components to arrive at a complete repair.
So any ideas on how to get to the root of the problems & is £1400 a fair price to cover supply & fit an upgraded boiler and to cover the 2 trips & 3 or 4 hours he has already spent here over a busy christmas period?
Thanks.........Paul
 
could be condensate pipe blocked and backing up into the heatexchager then leaking into fan??? anyone correct me if im wrong
 
your engineers a idiot,no you dont need a new boiler just some one who knows it,and tbh they dont come more simplified than a performa they can last up to 15 years so he is trying to rip you off
 
FIXTER,it cant on the performa,it has a fly by wire direct to detection on the condensate trap it will go to flame failure long before the fan fills up,the trap being a lot lower than the fan,the fly bys on top of the trap
 
Last edited by a moderator:
post some pictures of the leaks,i/we can tell you what it would cost to sort it probably only needs washers/o rings these cost a few quid,your boilers a long way from needing renewal
 
no problems fixter,the performa he being the same combi as the baxi 105 he and main 24/30 he all have this simple idea but it stops any damage if the conden blocks/freezes
 
yes simple screw trough the bottle,causes a continuity break on the detection circuit go,s strait to flame failure if you come across one of these boilers and think you have a condensate problem pull the white wire of the bottle and re set if its the cause it will run
 
now to pch the op please if possible get us those photos,i am afraid your engineer is trying to con you
 
gasman i had that problem the same today pulled wire off and it stayed on think the pipes are to close to an outside wall and freezing told the bloke to lagg them

gas man can you pour warm water down the flue on the baxi,s done it few times on worcesters but not on baxis
 
030.jpg032.jpg031.jpg

Sorry for poor pics, taken with camera with no flash in dark corner.
1st photo water was dripping from lower left of front of the boiler.
2nd photopart is on it's side, shows area of trunking above primary heat exchanger, there appeared to be leaks round hose type clip.
3rd photo shows pipe leading to primary heat exchanger after attempted fix with new O rings & lots of sealant.
Boiler now has "do not use sticker" on it
 
if its a 30 he or 24 he,it gets confusing with main as the band a,s are 30 or 24 eco he do you know if its a band a or b?
 
View attachment 1671View attachment 1670View attachment 1669

Sorry for poor pics, taken with camera with no flash in dark corner.
1st photo water was dripping from lower left of front of the boiler.
2nd photopart is on it's side, shows area of trunking above primary heat exchanger, there appeared to be leaks round hose type clip.
3rd photo shows pipe leading to primary heat exchanger after attempted fix with new O rings & lots of sealant.
Boiler now has "do not use sticker" on it

so the recupirater o rings are leaking? £3 each would take me 10 mins to change so if you were in my patch you would be charged £45 labour £6 parts the £45 inc filling/draining changing parts and de air locking if req,you defo dont need a new boiler but lets give the engineer the benefit of the doubt if you have a main heat exchanger leaking(highly unlikely) £110 20 mins to change if its the recupirator (even more unlikely its gone on the unions £85 parts 20 mins to change do you see where i am coming from?? its very likly you just need o rings so i strongly believe your engineers trying to rip you
 
i feel so strongly about this i would fit you in tomorrow on my last working day of the year if you were local i hate seeing so called engineers trying to rip people like your self off
 
View attachment 1671View attachment 1670View attachment 1669

Sorry for poor pics, taken with camera with no flash in dark corner.
1st photo water was dripping from lower left of front of the boiler.
2nd photopart is on it's side, shows area of trunking above primary heat exchanger, there appeared to be leaks round hose type clip.
3rd photo shows pipe leading to primary heat exchanger after attempted fix with new O rings & lots of sealant.
Boiler now has "do not use sticker" on it[/QUOTE


...........
 
Last edited by a moderator:
tbh in all my years of working on these boilers i have never failed to get a good seal on the o rings if used with silicone grease, i keep every single part in stock for this boiler including all the internal pipe work
 
I was giving him "the benefit of the doubt" as I am sure that he knows more of central heating boilers than I ever will, however I did not have confidence that he had actually been able to diagnose the problem & calculate the costs of repair against the cost of a new boiler.
He did quote £320.00 for a new primary heat exchanger, & did try to replace O rings to reseal one of the leaks, at one point water did seem to be coming from several points around the boiler.
I actually believe he was concerned this job could hang round his neck like a dead albatros as he did not know what had caused the leaks.

So if anyone round East London/South Essex wants the job, you would have my eternal gratitude...............Paul
 
come on fellas you know this is easily sortoutable any takers?????????,and no London would be a step to far even for me LOL
 
£320 for the main heat exchanger i know its London but he,s taking the p***
 
hey tom went up your way in the summer bullrings fun on the weekend
 
Status
Not open for further replies.

Similar plumbing topics

I
Yes press the button until there are 2 lights...
2 3
Replies
53
Views
6K
Deleted member 120897
D
Again, ongoing thanks. I'll have to get to my...
Replies
18
Views
2K
Thank you for the detailed and considered...
Replies
14
Views
1K
Good job buddy. Rather than a beer, if you’re...
Replies
24
Views
3K
Back
Top