Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Ecotec ignition failure f28 in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.

SlimD

Gas Engineer
Messages
67
Hi guys,
I'm after some advice from the more experienced gas guys.
I've been GasSafe for just over a year - qualified via an intensive course (which I know some of you guys have a downer on) after redundancy. I make no claims of understanding everything about boilers as a lot comes with experience and I'm intending to get on a boiler fault finding course to try and improve my knowledge but there's only so much you can do at once.
I have been to a Vaillant ecotec 824 today which is getting an f28 fault code. Gas supply is fine but ignition comes and goes with a fair bit of banging from burner chamber. I'm suspecting the gas valve but would appreciate any assistance anyone can give. Thanks in advance.
I've taken a video on my phone of the boiler trying to ignite but site won't support the file extension.
 
Sorted

And op try and upload it to a file site like photobucket etc
 
F28 can be lots of things.
Ionisation probe.
Ht lead
Blocked pump
Innefective pump.
Gas valve.
Pcb.
Blocked hex.
Frozen condensate

And others. I know you learning. But instead of guessing. Learn how to use a multimeter and fault find using the manufacturer flow chart.

Start with the obvious. Has the boiler being regularly serviced. If not ,it's probably ionisation, blocked burner.
Service th boiler and Follow MI and you can't go wrong. ( have you got a fga?

After that, you need to use your multimeter to diagnose further.
 
Sounds like resistance in the flue / chamber
 
F28 can be lots of things.
Ionisation probe.
Ht lead
Blocked pump
Innefective pump.
Gas valve.
Pcb.
Blocked hex.
Frozen condensate

And others. I know you learning. But instead of guessing. Learn how to use a multimeter and fault find using the manufacturer flow chart.

Start with the obvious. Has the boiler being regularly serviced. If not ,it's probably ionisation, blocked burner.
Service th boiler and Follow MI and you can't go wrong. ( have you got a fga?

After that, you need to use your multimeter to diagnose further.

Thanks Chalked. Yes got an analyser. I have a Multimeter but it is something I need to master. Using them is something that's covered on the faultfinding course I mentioned earlier.
 
Take out burner. And have a look inside. New gasket will be needed.
Check flue in entirety.
 
Also check gas pressures at meter and boiler. I had a Vaillant the other day running on and off on 6 mbar. Was making all kinds of random noises.
 
Looking closer at your video. Looks like the snorkel is trying to vacuum itself!
Have you tried taking it off the inlet? Could have collapsed inside.
 
does look like a gas issue to me to. Ever not enough from the meter or the gas valve

It does. If it was just explosive ignition and an F28 it would most likely be the electrode (gap probably). This does light straight away though doesn't it, then it seems erratic as if the valve is opening and closing. Could be a loose connection, Faulty solenoid, Board, etc. Hard to tell off video.
 
I did also get an f29 come up on one occasion, hence my thoughts it was the gas valve
 
Have you tried taking it off the inlet? Could have collapsed inside.
:confused: collapsed where ?


SlimD

its probably the gas valve mate , after that always check condense for f28

before changing try adjusting low co2 up by 1/8 of a turn just in case someone has tried having a go at adjusting it as have that a few times
 
Status
Not open for further replies.

Similar plumbing topics

Can I have your gas reg number please so I can...
Replies
1
Views
676
I've been to look at a boiler intermittent...
Replies
0
Views
1K
How are you getting on, anything to update?
2 3 4
Replies
98
Views
14K
  • Locked
Hi guys Unfortunately this thread needs...
2
Replies
33
Views
666
Back
Top