Doubtful, he said he's been having intermittent issues for the last 9 months. Although there could be other reasons for that to be causing issues that don't relate to the cold weather.What else throws up F28 in the depths of winter !!!
Could be if it is both or either, worth a check wouldn't you say?
I know it is not cold all year round but still produces, where does that pipe end up? Just a thought but would need to be on site.Doubtful, he said he's been having intermittent issues for the last 9 months. Although there could be other reasons for that to be causing issues that don't relate to the cold weather.
Nope, plumber or cadent gas has been out approx 20-30 times now.....Also I hope op is not testing the mbar
Not withstanding the F28, it would appear you have a you have 2 oversized boilers on a poorly designed system, I take it from the single large pump that there is no low loss header installed? (60kW through 28mm what were they thinking !!!)
Why haven't you gone back to the installer / manufacturer before now?
When you go down to reset, is it both that show the F28 ??
Have to ask as you wouldn’t believe the amount of people that think they know what they’re doingNope, plumber or cadent gas has been out approx 20-30 times now...
I’m based in Northwood Middlesex. Is there any recommendations that someone can make?
There's a superb engineer and troubleshooter in your area called Andrew Millward of https://www.homecomfortassured.co.uk/ive
Just do what he recommends, as said already sounds like the boilers are well oversized so could possibly be a poorly designed system with no LLH.
Why do you need two boilers for such a system with 30 kw each running in the same time? As mentioned above to all the others well oversized and get a reliable engineer or perhaps donit via warranty
I will second the post re Andrew, if anyone can Mr Millward can.
If you use Millward do keep us posted, thanks.
We sympathise with your frustration but do give him a chance to get back to you and make the necessary changes as occasionally a combination of events especially where electronics and sensors are concerned can lead to anomolies that aren't easily explained by a fault code. With an untracable intermittent fault it may eventually be a case of replacing parts in a systematic semi-educated way which is expensive but still no guarantee. Do continue to keep us updated as we're also on a learning curve albeit at your inconvenience, and goodluck hopefully you won't need it now Andrew is on the case.
I'm reluctant to tread on anybody toes mid-investigation, let it run it's course but this this would be my next areas of concern...
–There’s a problem with the gas supply to the boiler.
– [/s]There’s air in the pipes.
The pressure of the gas flow is too low.
–
– Igniter is defective.
– There is a fault in the gas valve.
– Electronics are defective.
can this fault also so be due to ignition leadSee above post again Navi, my strike throughs are like your boilers... unpredictable. It sounds like everything has been done with regards to your gas supply, F28 error includes gas + ignition so that side of things require further investigation imo hence recommending the igniter swap out. It may at this point ask Vaillant to participate again IF parts are required.
See above post again Navi, my strike throughs are like your boilers... unpredictable. It sounds like everything has been done with regards to your gas supply, F28 error includes gas + ignition so that side of things require further investigation imo hence recommending the igniter swap out. It may at this point ask be worth asking Vaillant to participate again IF parts are required.
The only baffling thing was one boiler will never switch off by itself, always both of them together at the exact same time.