A clamp on stat is more like the image furthest to the left.
The HW zone valve should close when the cylinder stat is satisfied. If the motorised valve isn’t closing it’s still getting a feed from somewhere. It could be a faulty cylinder stat or the cylinder stat isn’t connecting properly with the cylinder if it’s an open vented HW system?
 
A clamp on stat is more like the image furthest to the left.
The HW zone valve should close when the cylinder stat is satisfied. If the motorised valve isn’t closing it’s still getting a feed from somewhere. It could be a faulty cylinder stat or the cylinder stat isn’t connecting properly with the cylinder if it’s an open vented HW system?
Yes, I also learned that the zone valve for HW and zone valve for CH should both close if the cylinder stat and house setting temperature are satisfied, but only zone valve for CH closed when it reaches house setting temperature, but zone valve for HW NEVER close during programmer "on" period (when programmer setting time is off, then the zone valve for HW does close---so it this looks zone valve is no problem, right?)
My system is unvented cylinder system.
 
Does the HW zone valve close when HW programmed off?. if so maybe something as simple as the boiler temperature not set 5 to 10C higher than the cylinder stat, ie if cylinder stat set to 60C, boiler should be set to 65/70C.
 
It could be wired wrong, it could be a dodgy stat or not sitting on cylinder properly. A photo of the cylinder and stat would help.
John raises a good point as well. If the cylinder stat is set to 60°c then the boiler flow should be higher.
 
Does the HW zone valve close when HW programmed off?. if so maybe something as simple as the boiler temperature not set 5 to 10C higher than the cylinder stat, ie if cylinder stat set to 60C, boiler should be set to 65/70C.
HW zone valve indeed close when HW programmer is off.
But your comment does draw my attention: "the boiler temperature not set 5 to 10C higher than the cylinder stat, ie if cylinder stat set to 60C, boiler should be set to 65/70C."
Is this a must? Could you explain this theory?
I just checked my temperature settings:
Please see photo1 which is my boiler photo, that is central heating setting, right? according to photo 2 "setting temperature for your heating", I turned the knob to the position around 5 which is 74C;
My cylinder stat is set to close to 65C, maybe 60C, or 61C, or 62C, please see photo 3.
So based on your theory, my central heating temperature(74C) and cylinder stat temperature(60,1,2C) are correct?
 

Attachments

  • boiler lights.jpeg
    boiler lights.jpeg
    74.6 KB · Views: 14
  • heating temperature setting.png
    heating temperature setting.png
    83.3 KB · Views: 12
  • cylinder stat.jpeg
    cylinder stat.jpeg
    62.7 KB · Views: 16
It could be wired wrong, it could be a dodgy stat or not sitting on cylinder properly. A photo of the cylinder and stat would help.
John raises a good point as well. If the cylinder stat is set to 60°c then the boiler flow should be higher.
Please see attached photo of stat on cylinder and cylinder, if they are good to judge?
Please refer to my last reply to John that how I set the cylinder temperature and boiler heating temperature.
 

Attachments

  • cylinder stat.jpeg
    cylinder stat.jpeg
    62.7 KB · Views: 17
  • Cylinder.jpeg
    Cylinder.jpeg
    140.1 KB · Views: 16
The theory revolves around the first law of thermodynamics. Basically if the water leaving your boiler is max 60°c then the maximum temperature the water in the cylinder could ever be is 60°c. You have the cylinder stat at 65°c which in my opinion is 5°c too high because if you’re in a hard water area this temperature can cause lime scale to form. Set the cylinder stat to 60°c and leave the boiler at about 70°c. Any higher and you start to lose any condensing
 
The divisions on the cylinder stat are extraordinary at 6.66C/division just to create more of a challenge when setting it?.

Anyway, to test the stat, just turn it down and see if the HW cylinder zone valve closes while programmed on.
 
The theory revolves around the first law of thermodynamics. Basically if the water leaving your boiler is max 60°c then the maximum temperature the water in the cylinder could ever be is 60°c. You have the cylinder stat at 65°c which in my opinion is 5°c too high because if you’re in a hard water area this temperature can cause lime scale to form. Set the cylinder stat to 60°c and leave the boiler at about 70°c. Any higher and you start to lose any condensing
Thank you for letting me know this theory!
My cylinder stat is not set as 65°c, it is about 60-65°c. It is because between 65°c---45°c the gap is 20°c, there are 3 gaps, so i set it between 65°c and the next mark.
The reason I set on that position (60-65°c )is because I learned that the hot water should be set over 60°c in order to kill legionella bacteria. (as attached picture)
So for my cylinder stat temperature, I should/could turn the heating setting knob smaller, say between 4-5 to make it around 71°c ?(this attached photo2)
 

Attachments

  • hot water temprature.png
    hot water temprature.png
    484.8 KB · Views: 14
  • heating temperature setting.png
    heating temperature setting.png
    83.3 KB · Views: 17
The divisions on the cylinder stat are extraordinary at 6.66C/division just to create more of a challenge when setting it?.

Anyway, to test the stat, just turn it down and see if the HW cylinder zone valve closes while programmed on.
Exactly! Not sure why they designed and produced the stat like that!

Your solution to test the stat proved right! A few months ago, the very first time when we found the boiler was still firing even the programmer was off, the zone valve for hot water was opened, by chance, we turned the stat of the cylinder smaller, and saw the zone valve closed and boiler stopped, so at the time we could see the stat temperature setting seems working.
(then next time when it happened again: zone valve for hot water opened & boiler fired outside of programmer setting period, even if we turned the stat of cylinder smaller, boiler still continued to fire, so second time maybe zone valve issue.)
 
Yes legionella bacteria is killed off at 60°c. Yes set boiler control stat to that but no higher. The dew point for natural gas boilers starts at around 57°c, so your return water temperature needs to be that or lower, the lower the return temperature the greater the condensing. You also get greater condensing when the boiler is at part load but I won’t go into that now. If I was designing your system I would of done things a lot differently but that’s irrelevant now. As John says run his test to see what happens to the HW valve.
 
Re cylinder stat, with HW programmed on, turn stat down and note what its setting is, (check zone valve closing), turn stat back up slowly to reopen the zone valve, note the setting then turn it back down again to close the zone valve, gain note the setting, there should be ~ 5/8C differential.

Also see if the cylinder stat is located above the coil return from the cylinder.
 
Re cylinder stat, with HW programmed on, turn stat down and note what its setting is, (check zone valve closing), turn stat back up slowly to reopen the zone valve, note the setting then turn it back down again to close the zone valve, gain note the setting, there should be ~ 5/8C differential.

Also see if the cylinder stat is located above the coil return from the cylinder.
I got your point for how to turn and note the temperatures. That will have 3 temperatures?
i.e. 1st temperature: turn down when zone valve closes; 2nd temperature: turn up when zone valve opens; 3rd turn down again to close the zone valve.
So three temperature notes---to test what? Sorry I don't understand this?

Also see if the cylinder stat is located above the coil return from the cylinder.---is attached photo good to see? (if not, I can take another one)
 

Attachments

  • Cylinder.jpeg
    Cylinder.jpeg
    140.1 KB · Views: 15
Yes legionella bacteria is killed off at 60°c. Yes set boiler control stat to that but no higher. The dew point for natural gas boilers starts at around 57°c, so your return water temperature needs to be that or lower, the lower the return temperature the greater the condensing. You also get greater condensing when the boiler is at part load but I won’t go into that now. If I was designing your system I would of done things a lot differently but that’s irrelevant now. As John says run his test to see what happens to the HW valve.
so I am going to turn the boiler temperature control smaller, something between level 4--5, about 71°c, or 70°c or 72°c.
My installed system has caused me so much trouble..... I wonder how you would design it! Anything could be better!
The worse thing is the boss/gas engineer of my system does NOT know any of those questions I raised here........
 
I would set the boiler control knob to 5 which is a flow temp of 74°c ish.
If I was designing your system I would of designed a low temperature system with a boiler with good modulation and PDHW (priority domestic hot water) on either weather compensation or load compensation, that depends on a few things There are lots of advantages to low temperature heating systems. Less fuel consumption, better condensing, greater levels of comfort and cleaner air due to lower convection currents, better for the environment and so on. It is alarming that the boss of the company who installed this system is not fully clued up.
 
I got your point for how to turn and note the temperatures. That will have 3 temperatures?
i.e. 1st temperature: turn down when zone valve closes; 2nd temperature: turn up when zone valve opens; 3rd turn down again to close the zone valve.
So three temperature notes---to test what? Sorry I don't understand this?

Also see if the cylinder stat is located above the coil return from the cylinder.---is attached photo good to see? (if not, I can take another one)
I just want to ensure that the valve closes, re opens and closes again and also to check the cylinder stat differential (hysteresis) temperature between cut in and cut out.
I think the cylinder stat is located above the coil return from your photo.
 
I would set the boiler control knob to 5 which is a flow temp of 74°c ish.
If I was designing your system I would of designed a low temperature system with a boiler with good modulation and PDHW (priority domestic hot water) on either weather compensation or load compensation, that depends on a few things There are lots of advantages to low temperature heating systems. Less fuel consumption, better condensing, greater levels of comfort and cleaner air due to lower convection currents, better for the environment and so on. It is alarming that the boss of the company who installed this system is not fully clued up.
Right now it is 74°c(according to photo2), please see attached photo1. The stat on cylinder is between 60°c--65°c, something around 61°c?
So based on your theory should be 10°c higher, I should turn the boiler heating setting to around 71°c? (Turn to level 4 direction).

Your design looks good! But it is late now....

The boss's name and company are registered on the Wocester Bosch boiler website, so I picked him who should know the boiler system in theory!
The actual installation was done by his team member who left him, the boss did the commission.
But since I moved in, LOTS of problems happened! I can list 10 big issues here....
Worse of all, he came and checked, but he could not understand where/why gone wrong, I had to spend plenty of time here to get consultancy! I learn from you guys and got clearer answers than the one I paid over 5K for the system!!
 

Attachments

  • cylinder stat.jpeg
    cylinder stat.jpeg
    62.7 KB · Views: 10
  • heating temperature setting.png
    heating temperature setting.png
    83.3 KB · Views: 9
  • boiler lights.jpeg
    boiler lights.jpeg
    74.6 KB · Views: 15
Yes leave at those settings you mentioned above. Note if the rads struggle to get to temperature during extreme weather you may need to increase the flow temperature knob a bit but all these things should be considered during design stage. I’m not a fan of Worcester boilers personally but your system is installed now.
Most of us engineers on here are happy to help if possible. Myself and John here are passionate about what we do and if we can help and educate a little we will.
 
I just want to ensure that the valve closes, re opens and closes again and also to check the cylinder stat differential (hysteresis) temperature between cut in and cut out.
I think the cylinder stat is located above the coil return from your photo.

Re cylinder stat, with HW programmed on, turn stat down and note what its setting is, (check zone valve closing), turn stat back up slowly to reopen the zone valve, note the setting then turn it back down again to close the zone valve, gain note the setting, there should be ~ 5/8C differential.

Also see if the cylinder stat is located above the coil return from the cylinder.
Hi John, following your advice I have tested the stat and noted down each time temperatures. Please see below:

Photo1: turned down stat till heard "click", the zone valve for hot water was closing. The temperature is around 48°C;
Photo2: Turned up stat till heard "click", the zone valve for hot water was opening. The temperature is around 58°C;
Photo3: turned down stat till heard "click", the zone valve for hot water was closing. The temperature is around 48°C;
Photo4: Turned up stat till heard "click", the zone valve for hot water was opening. The temperature is around 58°C;

So, these mean the cylinder stat is working with no issue?

Thank you!
 

Attachments

  • cylinder stat1.jpeg
    cylinder stat1.jpeg
    64 KB · Views: 12
  • cylinder stat2.jpeg
    cylinder stat2.jpeg
    64 KB · Views: 9
  • cylinder stat3.jpeg
    cylinder stat3.jpeg
    62.2 KB · Views: 10
  • cylinder stat4.jpeg
    cylinder stat4.jpeg
    67.3 KB · Views: 11
Also see if the cylinder stat is located above the coil return from the cylinder.
Hi John,
Yesterday the photo maybe not clear, I have taken again for you to see if the cylinder stat is above coil return from the cylinder?
Thanks again!
 

Attachments

  • cylinder pipes1.jpeg
    cylinder pipes1.jpeg
    165.2 KB · Views: 11
  • cylinder pipes2.jpeg
    cylinder pipes2.jpeg
    110.9 KB · Views: 11
  • cylinder pipes3.jpeg
    cylinder pipes3.jpeg
    118.9 KB · Views: 11
Everything looks good to me
Everything---You mean both "stat on cylinder" and "if the cylinder stat is above coil return from the cylinder" are good?

Do you know "only nit pick is combo / inlet valve not above cylinder but that’s only a real issue when servicing cylinder just needs to be drained"---if this is an issue?

Thanks!
 

Similar plumbing topics

Thanks a lot for all your advice!
Replies
16
Views
5K
GREENSTAR CDi CLASSIC Worcester Bosch...
Replies
3
Views
729
Until the frost stat is satisfied then the...
Replies
7
Views
5K
Not if the cylinder is already satisfied, and...
2 3
Replies
52
Views
5K