Seen that happen Shaun quite a few times bud i had the same issue with the Worcester classic system I posted on here couple of months a go pipework was poorly installed cast your mind back I sealed it but as I said the working pressure was set to a bar not much more than a open vent system worcesters dont work on a pressure switch so you can run it on low system head low as 0.5 bar worth considering bud good luck kopNormally no inserts used
Excellent!
An old boy told me the pump will last longer if it is running on the cooler return water, hence the old way of doing it with the pump on the return. Don't bleed the rads with the pump running, though
Nos da
That wasn't one of your original options, but that would be OK.ive decided to put the pump on the return and keep the feed and vent to spec if it does pump over will give him the option to leave or seal it
I would guess they are old systems. I bought 1st house in 1972 which was piped like that, but it was going out of favour vs boiler - open vent - cold feed - pump then or shortly after, due to the issue of seesawing causing aerated water entry. I modified it, and piping was simpler as the cold feed point was then directly below the F/E tank.Virtually all open vent systems (except gravity to cylinder) I know of in my area are done with the vent off the flow at cylinder and feed off the cyl return.
That wasn't one of your original options, but that would be OK.
Should then be open vent - cold feed - pump - boiler. You definitely don't want the cold feed on the discharge side of the pump or there's a good chance there will be negative pressure somewhere, if pump DP is 8m.
As I'm sure you know, the open vent and cold feed should be no more than 150mm apart to avoid risk of over-pumping, but where they are in the circuit relative to other kit is irrelevant.
Not sure I understand that. It won't be under negative pressure if the cold feed is on the pump suction pipe.as it would be under neg pressure
Hard to say without knowing the details. You've clearly looked at lots of options so it's unlikely I can add anything, but I'm game to try if you want, no doubt others here will too.Can't get the vent and feed before pump unless it's on the return as it's an ab roof, which isn't the best as it won't vent if the boiler boils
Not sure I understand that. It won't be under negative pressure if the cold feed is on the pump suction pipe.
Hard to say without knowing the details. You've clearly looked at lots of options so it's unlikely I can add anything, but I'm game to try if you want, no doubt others here will too.
The bit about the boiler boiling - is it solid fuel? I didn't think boiling was an issue with gas or oil, as there are control and limit-stats.
I'd be a bit nervous with that arrangement. I did sketch below based on some assumptions:-pump on return pushing into boiler
feed on flow
vent on flow
What precautions are normally taken which you can't do on this job? I'm curious because it might apply to my house!there is an always risk in certain circumstances eg if a stat goes bad etc
Why not seal without pressurising. Use the header as top up, with gate and non return fitted. Sealed system controls as required with heat only or system boiler ( Worcester Cdi used to not need minimum pressure to operate, but check with them).
Non return is to stop the water backing up into the header. Therefore system controls required, i.e PRV and expansion vessel required either external or internal to boiler (system). Doesn’t need filling loop as header acts as top up vessel. Works a treat without stressing existing pipe work.
Have got two systems like this operational now in their sixth year and no problems.yea but would it open under gravity and not stick
Have got two systems like this operational now in their sixth year and no problems.
Top of system for header. Followed by gate or lever in downfeed, so you can turn system of and for easy replacement of check valve. I positioned them in airing cupboard. Check valve can be anywhere between isolation valve and where it tees into the system.
Not sure how to read that?Trying to work out how much head you have
Does the gate valve stay open in normal operation?Use the header as top up, with gate and non return fitted.
I converted mine about 20 years back. Old cast iron floorstanding boiler, gravity HW, pump next to boiler, pumping downwards. No controls. Cold feed to boiler return.I am actually having the same problem trying to decide how I convert a gravity hot water/pumped rads to all pumped on a very old system, without pump over or corrosion.
Gate valve stays open. Ans yes you can just seal, add vessel and PRV and have virtually no pressure. Its just convenient using the existing header instead of a filling loop if its already there.Does the gate valve stay open in normal operation?
I can't see how this differs from just having an expansion vessel, but with pre-charge pressure somewhat lower than normal.
Still need to put the expansion vessel connection in the right place, to avoid having negative pressure somewhere.
OK thanksGate valve stays open. Ans yes you can just seal, add vessel and PRV and have virtually no pressure. Its just convenient using the existing header instead of a filling loop if its already there.