Freezing 3yr old son's bedroom HELP! | Plumbing Jobs | The Job-board | Page 3 | Plumbers Forums

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

American Visitor?

Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Freezing 3yr old son's bedroom HELP! in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.
if you can pass the initiation test and pay the fee im sure crop will give your a brand
 
if you can pass the initiation test and pay the fee im sure crop will give your a brand

What like a sheep brand you mean? Er, no thanks I`ll pass on that !!!!

I am an engineer you know, got papers to prove it and my dad showed me the difference between an adjustable, open ended and ring spanner when I was 10 or 11 and he showed me the correct way of winding ptfe tape around a barrel nipple so do I qualify now ?
 
What like a sheep brand you mean? Er, no thanks I`ll pass on that !!!!

I am an engineer you know, got papers to prove it and my dad showed me the difference between an adjustable, open ended and ring spanner when I was 10 or 11 and he showed me the correct way of winding ptfe tape around a barrel nipple so do I qualify now ?

its a must it doesnt hurt that much and maybe but the donation will have to be bigger
 
I think I will wait until the OP gets his problem solved before I comment further.

I think if the OP hasn't got heat into the bedroom by now, then his 3 year old son must have frozen to death.
 
Update:

I have a HIVE thermostat, so turned the heating on from work at 4pm. Got home about 6pm, problem rads still showing top middle tems of 48 lounge and 53 bedroom respectively. Inlet pipe red hot (well 65 anyway with flow from boiler showing 70 using IR thermometer so prob slightly higher in real life). Hot rad close to boiler showing 65 degrees and rest "felt" good a hot. So no miracles occuring over night obvioulsy.

By the time kids were fed and watered it was 6:45 and so quickly decided to try the HIT IT & WAGGLE IT SOLUTI0NS ..............

1. TAPPED PIN HEAD WITH HAMMER 3 TIMES;
2. Tapped side of valve a couple of times;
3. grabbed pin with needle nose pliers and pushed up then pulled down on ping and, finally
4. gave the pin a waggle side to side 12-6 then 3 - 9 oclock before pressing up/down again;

For good measure also tapped lockshield valves and screwed closed, fully opened again........

No IMMEDIATE rocketing of system temperature, damn it (I thought -by now lounge up to 50 and bedroom up to 55 as 45 min has elaspsed with heating on full blast as set room thermostat to 25 at 4pm). Went and bathed kids, 20-min later front room and bedroom pretty much the same +couple of degrees more if that. Remembered over the weekend father in law suggested I set heating pump to no2 speed. Thought stuff it, give the system a blast and so quickly turned pump back to no3 (max speed) - which is actually what Vokera technical help guy told me to set the pump at today, without justifying his statement, when I explained the hassle I was having. Net result, within 10-min bedroom rad up to 60-degrees and front room up to 55degrees.

Has this solved it? - Not convinced to be honest and will need to wait until tomorrow AM to see as remember the rads will eventually warm up if you leave the heating on long enough (like 4 hours) and by this time the system had been blasting on full heat for 3 1/2 hours!

So sorry, but no conclusive proof of system solution (yet). One downside is at Pump setting 3 I now have 10-degree temp difference at boiler between flow and return. Not surpirsing as 8 of the downstairs rads are throttled right down to try and push heat to the rads at end of line. One thing I am certain of is turning the pump to #3 sped up the rate of heating of the problem rads (duh).

Once I solve the problem rads slow heating rate and get them to max temp same as the rest, (60-degrees within 30-min is my target for "success" based on his brothers bedroom radiator performing like this) I will balance the system again to try and get 20-degree temp drop at the boiler (55 return on 75 flow temp) as apparently this increases chances of condensing function working......

Will update tomorrow when Ive seen performance from a cold start.
 
p.s. system has been on pump setting 3 for the last 18-m (when i bought the house) and only changes to speed 2 at the weekend after father in law was round, so prior to tonight the system still failed to heat up the problem rads when pump was on 3. I therfore wonder if the valve tapping has helped................tomorrow AM will tell.

Kid not frozen (yet) and sound asleep in cosy bedroom thanks to the last 4 hrs of heating!!
 
p.p.s - I see there was some "friction" in the forum between members. All I will say is I appreciate everyone's feedback and thank you all for taking time to try and help out, be that from the position of practicing "certified" engineer or experienced homeowner who has faced similar issues.
 
Just a few quick questions, I haven't read the the full op. So if you've answered this already, sorry.

Has it ever worked, does it have a cylinder on it? Does the system perform better with the hot water demand satisfied or even off?
Was the system designed and fitted all at the same time? Or added on to with an extension or
Like?
Are you sure the nest is calling for heat all the time? And are there zone valves? All these will have a factor on you system.
 
Valves red hot. Radiators cool. Trv stuck. Hit it harder. You will see immediate result, unless not hitting it hard enough. Hit it harder.
 
Never worked in my view. Home purchased after previous owner renovated from 2 bed to 4 bed bungalo (extended in every direction you can think of). So dont know if all rads were added to the system when the boiler was installed (2010) according to home report or after final building works complete in 2012. I suspect rads were added, but upstairs they all have teh same PVC pipework (15mm diameter) and are identical rads, so might all have been done at the same time. Just dont know.

35kw vokera compact he Comi boiler, so no cylinder.........(sorry not really sure what you are asking)

not looked at performance when hot water demand is ON, as every test I perform I make sure no one turns on the hot water or goes for bath/shower to max heat into t he rads

No zone valves in the system and certain the HIVE system is calling for heat as thermostat set well above room temps in my tests (as I type I wonder if the boiler is reaching the set water temp (70 odd degrees) and cutting out - but again, doesnt explain why his brothers radiator 8ft away in another bedroom shoots up to 65 degrees in no time yet problem rad is still 50 degrees after a couple of hours normally - so I do think the system is calling for heat constantly
 
Valves red hot. Radiators cool. Trv stuck. Hit it harder. You will see immediate result, unless not hitting it hard enough. Hit it harder.

Exactly! Nearly always that's all it is. I have to whack them TRV pins hard sometimes.
And it can be inside the body of the TRV and the only way to fix it properly is replace the TRV.
I know it can also be the internal 'pin' seized, which ain't fixable.
Balancing is possible to be the main issue if problem ALWAYS was there, but not otherwise.
 
Yep. Beat the snot out of it till it works as a makeshift. Dump pressure snatch two new trv's and jobs sorted. 5 pages later.
 
If it's a combi, the pump should be on 3. Replace the trv,s and go from there.
 
p.s only addressing this now as always thought the insulation in the boys room was the issue and so improved that first, which I did last summer and before having a IR thermometer. Brothers room is toasty warm now, but 3yr olds is freezing in morning. Homed in on rad issue afetr buying an IR thermometer to directly compare two rads, and was shocked at how much difference between the two with 8ft separation (10+ degrees typically)
 
No zone valves in the system and certain the HIVE system is calling for heat as thermostat set well above room temps in my tests (as I type I wonder if the boiler is reaching the set water temp (70 odd degrees) and cutting out - but again, doesnt explain why his brothers radiator 8ft away in another bedroom shoots up to 65 degrees in no time yet problem rad is still 50 degrees after a couple of hours normally - so I do think the system is calling for heat constantly

Either get the TRV pin thumped with a hammer or whole valve replaced.
By all means fire ahead with a basic balancing of system, - try turning the lockshield valves nearly off on nearby rads that are heating very fast.
Ignore all the technical talk. You are trying to get a radiator improved that has never worked fully. That should have been narrowed down to what is likely wrong, or fixed - a couple of days ago.
 
Can I just ask one more favour - Im seeing 1.25 bar pressure rise from cold to hot and have a cold pressure of 1bar, hot goes just over 2bar after 3 1/2 hours tonight. Does this indicate I should check/re-pressurise the expansion vessel or is +1bar from heating acceptable? The vokera 35h EV should be at 1bar.

If I test the EV, I understand the system should be drained of water (so diaphragm has air on both sides) is this correct?

Just trying to get as many jobs done at one time if the system does need draining of all water (not sure if it does for these two jobs -TRV replacement and EV checking).
 
You are supposed to get the expansion vessel air charge checked minimum once a year when boiler is serviced.
Remember you can't open the gas boiler or work on it unless you are gas qualified.
Separate expansion vessel is a different story.
 
Can I just ask one more favour - Im seeing 1.25 bar pressure rise from cold to hot and have a cold pressure of 1bar, hot goes just over 2bar after 3 1/2 hours tonight. Does this indicate I should check/re-pressurise the expansion vessel or is +1bar from heating acceptable? The vokera 35h EV should be at 1bar.

If I test the EV, I understand the system should be drained of water (so diaphragm has air on both sides) is this correct?

Just trying to get as many jobs done at one time if the system does need draining of all water (not sure if it does for these two jobs -TRV replacement and EV checking).

If the case has to come off you can't do that without being gsr.
 
You are supposed to get the expansion vessel air charge checked minimum once a year when boiler is serviced.
Remember you can't open the gas boiler or work on it unless you are gas qualified.
Separate expansion vessel is a different story.

The gas guys are lazy best :) its only us oilies that check the ev on a service :) :) :)
 
The gas guys are lazy best :) its only us oilies that check the ev on a service :) :) :)

Tell me about it! :smile: I am overworked sometimes on oil. I wish all I had to do is service or replace them wee easy gas boilers.
 
Tell me about it! :smile: I am overworked sometimes on oil. I wish all I had to do is service or replace them wee easy gas boilers.

The gas stuff may a bit technical.:Angel_anim:
 
The gas stuff may a bit technical.:Angel_anim:

I must admit the gas stuff must be very technical. That's probably why I have to tell people where their gas engineers failed. :smile:
That Goose bloke is a gas engineer and seems to be lost in the complexity of basic oil stuff. :grin:
 
The gas stuff may a bit technical.:Angel_anim:

I would love to see you sorting an oil twin vapour burner rayburn nouvelle in less than 3 hours on a standard service, or 3 days if you've not got a manual
 
Status
Not open for further replies.

Similar plumbing topics

I will have to experiment like you said and...
Replies
6
Views
935
  • Question
Will be a 15-60 then prob ups2 Green lights ?
Replies
8
Views
968
well, I really cannot see what extra features...
Replies
10
Views
1K
1/4 turn black knob on both. open bleed screw...
Replies
7
Views
861
Below is a sizing chart based on a heat loss...
Replies
1
Views
798
Back
Top