Evening all, your thoughts please...
Friend of the family had trouble with heating last week. System is y plan. Went round no water in system.
Cleared blocked cold feed, filled system and tested all good.
Called today no hot water. Went to look. Call for hot water and mid position valve moves over correctly yet pump does not start.
Switch to heating, valve moves over and boiler fires all good. Put both on, valve moves to mid position, boiler goes out. As soon as hot water is selected regardless of what heating is doing the boiler shuts off.
Cant be cylinder stat or programmer could it? And have power off orange on mid position valve. So surely not that.
Stumped on this one anyone have any ideas?
Thanks in advance!