Honeywell ABV setting | Plumbing Jobs | The Job-board | Page 2 | Plumbers Forums
  • Welcome to PlumbersTalk.net

    Welcome to Plumbers' Talk | The new domain for UKPF / Plumbers Forums. Login with your existing details they should all work fine. Please checkout the PT Updates Forum

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

American Visitor?

Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Honeywell ABV setting in the Plumbing Jobs | The Job-board area at Plumbers Forums

A wet Sunday, so I thought I would have a look for ball valves with an integral flow meter or with plug-in fixed-flow cartridges. Assuming that the Viessmann 100 WB1B’s minimum flow rate of 200 l/h is acceptable also as a minimum flow for pump overrun, it would be a trivial job to replace the Honeywell DU144 ABV by a simple fixed-flow ball valve such as Cottam’s CP961 (22mm) with a 4 l/min low-pressure cartridge – rated up to 85degC. Are these suitable for CH systems or are they intended for (colder) DHW and I should look elsewhere?
 
On this wet Sunday you could have drained your system altered the pipe work so the boiler was able to circulate to a pair of close coupled tees. Put the large Grundfos on the system just after them & set it to auto, refilled your system & been sitting down with a drink admiring your handy work with a boiler running perfectly. (as suggested in post 7)
The 100 WB with a small pump set to a speed to over come the heat exchangers resistance & short pipework loop to the tees will look after itself & any pump overrun. The main system pump wired from the switch lives & set to auto will look after the system as the flow rates change.
Job done or am I missing something?
 
A wet Sunday, so I thought I would have a look for ball valves with an integral flow meter or with plug-in fixed-flow cartridges. Assuming that the Viessmann 100 WB1B’s minimum flow rate of 200 l/h is acceptable also as a minimum flow for pump overrun, it would be a trivial job to replace the Honeywell DU144 ABV by a simple fixed-flow ball valve such as Cottam’s CP961 (22mm) with a 4 l/min low-pressure cartridge – rated up to 85degC. Are these suitable for CH systems or are they intended for (colder) DHW and I should look elsewhere?

It looks OK temperature wise, but since you don't know the valve coefficient (Cv), you may end up having to throttle it to give that 4 LPM@6M head.
What's wrong with your present "Towel Rail" bypass?.
 
The serendipitous towel rail bypass is working fine!

But the Honeywell DU144 ABV is also inline and is open even at its highest setting, so in a rare idle moment I was looking at an inexpensive but reliable replacement that would give the constant minimum flow for the boiler on pump overrun. I could of course just replace it by a shut a gate valve, for use only when draining the system.

Your comment about the Cv intrigues me (a person of admittedly little brain): if such a valve is working within its rated pressure range (the low pressure cartridges are 0.2 - 4 bar, and the zero-flow head of the lowest of the UPS pump’s six modes is about 2.2m head), why please would it not give a 4l/m bypass all the time, including on pump overrun?
 
You might please post the pump data sheet again as I don,t seem to be able to easily locate it.
EDIT: OK found them, thanks.

You are running on speed 1 which in effect is a 6M constant head between 0 & 2.3 M3/hr?, the ABV on its highest setting of 0.6 = 6M will not pass any water as it will be closed, have you set it to this index?. If you require to run on a higher pump head then it will start passing, therefore the need for possible removal.

Re the cottam's valve, again I cannot find any technical data on this (the data sheet is blank) but the only way that this will maintain a constant flow rate of 4 LPM between 0.2 and 4 bar is if it is a very clever control valve (akin to a ABV but even better.) If it is a fairly common type ball valve then it will have a certain flow rate (its Cv) in m3/hr @ 1 bar differential pressure, knowing this you can calculate the different flow rates for any given differential head. (Flow is prop. to sqrt head).
Again if you have any data on this please post.
 
Last edited:
The UPS2 25-80 is not suitable for your system as it will always be working in the constant pressure part of the pump curve. This is fine for underfloor heating, but not for radiator systems where the rads are turned on and off by TRVs. With a constant pressure an automatic bypass valve will be either permanently closed or permanently open depending on its setting.
 
The data spec I was looking at on Cottam's CP961 is attached. Their website has several similar ones, differentiated by the end connection (BSP x 2, compression x 2, ..).
 

Attachments

  • Cottam CP961CC.pdf
    668.2 KB · Views: 27
Its not ideal but will certainly work (and is), decomplexity requires a minimum flow rate of 4 LPM so the ABV if set to index 0.55/0.56 will (theoretically) achieve this at a 6M head but as you observe there will be a constant bypass flow of 4 LPM at all times. PP (proportional pressure) mode is the most economical way of running but because of its very nature the ABV will "perform even worse" under these conditions, if one assumes that a PP1 setting is required (2.2 to 6.0M) then IF the ABV is set up to pass 4 LPM @2.2M, index setting 0.2, it will pass ~ 21 LPM @ 6m, completely unacceptable. A fixed by pass, if set up to pass 4 [email protected] will "only" pass 6.6 LPM@ 6M, a far better proposition. OR the existing towel rail can (and is) be used which is plumbed in flow/return; downstream/upstream of any zone valves etc so is in the circuit on pump overrun and will not interfere with the condensing efficiency to any significant amount.
I am surprised that the boiler makers havn't introduced some logic in their systems to open a dedicated MV based on minimum flow/pump overrun etc.
 
Last edited:
The data spec I was looking at on Cottam's CP961 is attached. Their website has several similar ones, differentiated by the end connection (BSP x 2, compression x 2, ..).
Thanks, I've seen those, I will be very impressed if that will control the flow rate automatically, might be worth giving their technical dept. a buzz?.
 
There for limiting water flow eg cold and hot

Won’t be any good on heating and will short circuit as always open
 
Yes but the "wondervalve" above claims that it will (or might) maintain a fixed flow with a varying pump head as will occur with PP operation. The setter valve is recommended for a pump on a CP (constant pressure) setting but the flow would vary in pump PP mode?.
 
Grundfos's note (attached) on their newish Alpha2 pumps and ABVs in CP and PP modes is worth a look. The parting comment there (for PP mode) is that "If an automatic bypass valve must be used, then a manual fixed bypass valve should be installed in series with the automatic bypass valve. The fixed manual bypass will restrict the flow as the automatic bypass valve opens."
 

Attachments

  • Grundfos Alpha2 and ABVs.pdf
    167.4 KB · Views: 57
Grundfos's note (attached) on their newish Alpha2 pumps and ABVs in CP and PP modes is worth a look. The parting comment there (for PP mode) is that "If an automatic bypass valve must be used, then a manual fixed bypass valve should be installed in series with the automatic bypass valve. The fixed manual bypass will restrict the flow as the automatic bypass valve opens."

I don't see any advantage in having a ABV+fixed bypass over a fixed bypass alone. See my post #10.
The wondervalve may improve this again, it will be interesting when/if they reply to your email.
 
Agreed - I found their argument a bit strange. It appears that the only circumstance where a differential pressure driven ABV would be effective is where the pump has a monotonically decreasing head from zero flow onwards. And none of Grundfos's domestic pumps have this as far as I know.
 

Similar plumbing topics

Any gas boiler's HEX can stand a static head...
Replies
16
Views
1K
  • Question
With the system as it is at the moment, I'd...
Replies
6
Views
2K
The DU145 is the angled version so wonder why...
Replies
1
Views
427
Everything working fine on PP mode - thanks...
Replies
7
Views
914
The Honeywell VT5005T referred to (in a link)...
2
Replies
30
Views
8K
Back
Top