Installer installed undersized radiators | Plumbing Jobs | The Job-board | Page 3 | Plumbers Forums

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

American Visitor?

Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Installer installed undersized radiators in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.
For you guys that do it, how much would you roughly charge to change from a single to a double (same size) labour only?

Also, where is the best place to buy (non trade only) cheap rads?
 
Living room: 3.4m x 3.7m x 2.7m Rad installed: 1000mm x 600mm single BTU 3238
Bedroom 1: 3.5 x 3.4 x 2.6 Rad installed: 900mm x 450mm single BTU 2262
Bedroom 2: 3.77 x 2.5 x 2.65 Rad installed: 700mm x 450mm BTU 2007

Living room 7000 btu
bed 1 6000 btu
bed 2 5000 btu
without calculating walls/ windows/ insulation etc.
 
For you guys that do it, how much would you roughly charge to change from a single to a double (same size) labour only?

Also, where is the best place to buy (non trade only) cheap rads?

where are you based?
 
put a request here [DLMURL="http://www.ukplumbersforums.co.uk/im-looking-plumber-gas-engineer/"]I'm looking for a Plumber or Gas Engineer[/DLMURL] for someone local to you who can come and advise you
 
Get some prices for the work, I would get labour & rads price.
the installer can probably get cheaper rads and offer a guarantee against what he does. I do not give guarantees on anything I have not supplied.
if you have it done again you want it done correctly.
post it up in the forum and somebody will help you out.
 
I will give you another tip don't try and save money on rads and buy em from screwfix or b&q because you won't save, gonna cost even more in the long run
 
Last edited:
If you want to get the rads your self I am sure your buddy will fit them for you !
If you want a profesional do as Steve b say list your location and you will hear from a profesional plumber who will come an survey job for you !
 
I will give you another tip don't try and save money on rads and buy em from screwfix or b&q because you won't save, gonna cost even more in the long run

why do you say that? think this should be a seperate thread but surely made of same metal and come with 10 year guarantee (which merchants dont have). but nearly £30 cheaper per rad, so curious why you dont recommend them!
 
Living room: 3.4m x 3.7m x 2.7m Rad installed: 1000mm x 600mm single BTU 3238
Bedroom 1: 3.5 x 3.4 x 2.6 Rad installed: 900mm x 450mm single BTU 2262
Bedroom 2: 3.77 x 2.5 x 2.65 Rad installed: 700mm x 450mm BTU 2007

Living room 7000 btu
bed 1 6000 btu
bed 2 5000 btu
without calculating walls/ windows/ insulation etc.

Wow those are a lot higher than my calcs are suggesting

Mine is
Living room: 5000 btu
bed 1 3700 btu
bed 2 3000 btu

where are you based?

east midlands

I will give you another tip don't try and save money on rads and buy em from screwfix or b&q because you won't save, gonna cost even more in the long run

Are they really that bad. I was going to get them from Screwfix but they don't have the right size. What's wrong with them?

If you want to get the rads your self I am sure your buddy will fit them for you !
If you want a profesional do as Steve b say list your location and you will hear from a profesional plumber who will come an survey job for you !

The thing is that he has offered t do some of it labour free so I have to take it, don't I?
 
I wouldn't go there again. He is probably doing this over and over to customers similar to you.
bin him and get the job done correct.
 
Over sizing radiators can also be just as bad as under sizing as it will affect efficiency and correct temp returns of these new condensing boilers
 
its not just as bad as customer is warm in there own home, which surely is what we are meant to be doing as "heating engineers" however it is still bad as it will cost more then it should to heat the home.
but as someone said before this would be my estimates as i can not see window/ insulation etc.
 
pay peanuts get monkeys your wasting your time pursuing this legally after a year better to spend the extra for some bigger rads and treat it as one of lifes little lessons always get 3 or 4 quotes to get some idea of what the right price for a job is also always get something in writting as to what your getting for the money and what it will do once fitted
 
Last edited:
he went for the B&B option then changed his mind and camped:)
For the first time in his life...
In the 5 pounds Argos single season sleeping bag in the current Lake District conditions (-6C, 35mph), 700m above see level on the eastern side of Skaffel Pike :)

Anyway, I assume that any serious user calling himself diyer should know how to do compression/threaded joints.
Have a look on the youtube, get a double convector rad(s), and have a go.
Best with good competent plumber for the first time.
And keep in mind, that plastics doesn't like high flow temperatures for long time... And the underfloor leaks may go undetected for a while...
 
Over sizing radiators can also be just as bad as under sizing as it will affect efficiency and correct temp returns of these new condensing boilers
@Chris: You put a like on this comment? Oversizing allows you to lower the flow temperature and therefore minimising heat losses and maximising the gains from the latent heat.

Could someone explain to me the negative effects to expect (except customer spending more on the radiators)? As long as the oversizing is done equally I could not see negative effects at all.
 
@Chris: You put a like on this comment? Oversizing allows you to lower the flow temperature and therefore minimising heat losses and maximising the gains from the latent heat.

Could someone explain to me the negative effects to expect (except customer spending more on the radiators)? As long as the oversizing is done equally I could not see negative effects at all.

Well for one building control can and so fail new houses as not energy efficient
 
It's all about energy efficiency at the boiler so it will condense efficiently and use less gas or use it better thus saving the planet . the flow and returns at the boiler must only have 10c temp difference so if the rads are too big for the boiler then the return to the boiler will be too cold and then the boiler won't condense . Which means you might as well not fit condensing boiler, as stated building regs can now make you rip it all out if they get involved. I'm not the best explainer so hope this is good enough. If you've done level3 about modern system design this should have been taught at that stage.
 
It's all about energy efficiency at the boiler so it will condense efficiently and use less gas or use it better thus saving the planet . the flow and returns at the boiler must only have 20ºc temp difference so if the rads are too big for the boiler then the return to the boiler will be too cold and then the boiler won't condense . Which means you might as well not fit condensing boiler, as stated building regs can now make you rip it all out if they get involved. I'm not the best explainer so hope this is good enough. If you've done level3 about modern system design this should have been taught at that stage.

You are getting things a bit back to front here.

I've also corrected a bit for you
 
Defo think its 10c but going to check later.
Also what bits back to front tamz
 
Defo think its 10c but going to check later.
Also what bits back to front tamz

First of all the lower the return temperature the higher the condensing effect. Anything above 70 degC has to be considered as non condensing range.
The lower the flow temperature the lesser the heat radiation part and therefore the lesser the heat losses in specific in conventional buildings with non reflective membranes, corroded ones or none at all.

The spread only influences the amount of heat distributed into the room. If you use a 55/45 design temperature the spread will obviously be 10 degC. Same on a more extreme 40/30. If you get to lower design temps you will not be able to have a great spread anymore which automatically increases your radiators beyond the increase due to the lower temperatures.

If you go for 60/40 you can keep your rads and pipes smaller but typically your heating pump has to work longer and harder as the friction will be higher. Thus can lead to not being able to use the VP modes on the hopefully A rated pump. The longer boiler run times will also increase losses through the flue. In conjunction with an oversized boiler this will be anything but green.

As far as building control goes they should then fail all surface heatings and heat pump systems? How would they be bothered by bigger and therefore more efficient radiators?
That casts a funny light on those guys waving through uncommissioned boilers being fitted to no standards and not even working.
 
Last edited by a moderator:
I'll save you the trouble of looking
Older systems were based on an 11º drop. New systems on condensing boilers should be set for a 20º drop.
Condensing boilers only condense when the return temperature is below 55º. This requires oversized rads or a low flow rate and careful balancing.
Big rads that feel cool to touch and low return temperatures mean cheaper bills.
 
Have you got shares in Grundfos Dirk :lol:
Btw most bco's (and i'm sure we have met the same ones) couldn't tell the difference between a paraffin heater and a boiler
 
I'll save you the trouble of looking
Older systems were based on an 11º drop. New systems on condensing boilers should be set for a 20º drop.
Condensing boilers only condense when the return temperature is below 55º. This requires oversized rads or a low flow rate and careful balancing.
Big rads that feel cool to touch and low return temperatures mean cheaper bills.
I should learn from you to keep things short and simple.
 
Status
Not open for further replies.

Similar plumbing topics

  • Question
It shouldn't make any noticeable difference id...
Replies
1
Views
621
  • Question
Are those outputs at the same delta T? 125...
Replies
4
Views
696
Below is a sizing chart based on a heat loss...
Replies
1
Views
798
Each manifold will have it's own pump and TMV...
Replies
7
Views
986
Back
Top