You can have fluctuations with the pipework temperature, but in rare circumstances you could have let by from the ecv and a leak at the same rate, so it shows no drop but there is a leak, in two places. You would be unlucky to get that. But if in doubt, unscrew the governor and spray leak detector into the closed ecv.
if you have a leak rate at the same rate as the ecv lets by this is why you do let by at 10mb and TT at 20mb, so that the leak will show on the TT, as it is being done at a different pressure