Ok.. so back to the original job on this post..
I fitted a Vaillant 30kW system boiler and upped the pipework in 28mm from meter to boiler as boiler and hob wasn't getting enough gas
I've now added a test point to both boiler and hob. I've also teed the hob off the 28 which I brought further up underneath the boiler..
I added the test point on the 15mm.. so!
Standing @ meter 25mb
WP @ meter both app 21mb
WP @ meter 1 app 21.5mb
WP @ boiler test point 20mb
WP @ hob test point 20mb
WP @ boiler with hob on 19mb
WP @ hob with boiler on 19mb
Have told custard to replace hob as burners went out with just hob on- hob is 30 years old.
I expected to see a working pressure of 20 at both appliances when both on.
Pipework is not undersized.
Why am I only getting 19????
These are my pipe calculations for what's currently there..