Low gas pressure | Gas Engineers Forum | Page 5 | Plumbers Forums
  • Welcome to PlumbersTalk.net

    Welcome to Plumbers' Talk | The new domain for UKPF / Plumbers Forums. Login with your existing details they should all work fine. Please checkout the PT Updates Forum

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

American Visitor?

Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Low gas pressure in the Gas Engineers Forum area at Plumbers Forums

Status
Not open for further replies.
Nope your looking at the tables wrong. That 2.9m3 refers to a 3m length of 15mm with a 1mb drop.
A mere 20 cm section would flow alot more than that...by my loose reckoning easily in excess of 5m3

I wasn't looking at a table. I was using the mr combi pipe size app and for the length of 15 I have with 1 elbow you won't get higher, needs to be 22

ceeca4987ac4bf7f57e40853133693df.jpg


9410c5b79e6e2a1fdacbd3cefb2fa479.jpg
 
Last edited:
Why not put a reducer on the connection from the boiler and take it straight to 22 or 28? That's what I do with boilers which have 15mm connections. I would also tee the hob off either the 22 or 28mm pipe.
 
App. and Tables in agreement 2.9 flow gives 3 meters and 20 meters for 15 &22.
Length 700mm pressure drop 700/3000 & 700/20000 which equates to the 0.233 & 0.035 given by App.
Phil also right with flow through 700mm length of 15mm. 1/4 of 3 meter length could be expected to give double the 3 meter flow, ( L X Q X Q approx constant).
 
App. and Tables in agreement 2.9 flow gives 3 meters and 20 meters for 15 &22.
Length 700mm pressure drop 700/3000 & 700/20000 which equates to the 0.233 & 0.035 given by App.
Phil also right with flow through 700mm length of 15mm. 1/4 of 3 meter length could be expected to give double the 3 meter flow, ( L X Q X Q approx constant).

Why does the app say for 2.91 with an effective length of 700mm you need 22?
 
Why not put a reducer on the connection from the boiler and take it straight to 22 or 28? That's what I do with boilers which have 15mm connections. I would also tee the hob off either the 22 or 28mm pipe.

I will do from now on! But from what Phil and Joni say I should get enough flow from that short run of 15 ... so what gives?
 
Can you upload a drawing. Something doesnt add up here from what youv'e said.
 
Sorry if you have answered this before, but what is the working pressure at the meter?
 
I dont use apps or rather put an over reliance on them. Pen and paper is best. But ive downloaded one that says different anyway which is more in line with my ready reckoning.

And 30kw is 30kw wether its vaillant, ideal or heatline - its not the boiler. As this demonstrates that small bit of run can handle upto a theoretical 45 ish kilowat

Edit.
Yep accurate drawing of the run.


88eb41eeaf34feb9215e52b32e81ca7a.jpg
 
Last edited by a moderator:
I dont use apps or rather put an over reliance on them. Pen and paper is best. But ive downloaded one that says different anyway which is more in line with my ready reckoning.

And 30kw is 30kw wether its vaillant, ideal or heatline - its not the boiler. As this demonstrates that small bit of run can handle upto a theoretical 45 ish kilowat

Edit.
Yep accurate drawing of the run.


88eb41eeaf34feb9215e52b32e81ca7a.jpg

What app is that Phil?

Agreed re: heat input ratings.. I've tried drawing it and my drawings are confusing.. but basically there are 24 elbows, 2 45s and approx 14 meters of 28mm.
 
Very experienced Gas Engineer was perplexed to be reading 16 at meter with his brand new certified digital manometer. Explanation, it was set for mmHg instead of mbar. Trust nothing at first sight.
 
Very experienced Gas Engineer was perplexed to be reading 16 at meter with his brand new certified digital manometer. Explanation, it was set for mmHg instead of mbar. Trust nothing at first sight.

Lol oh dear!! I used a manual wet u-gauge though
 
I cant put that into a visual way.

But all id say is if youve teed off the 15mm to the hob - I wouldn't have done that. Id have teed off the 28 to the hob and left that final 15mm run to the boiler unimpinged.
 
I cant put that into a visual way.

But all id say is if youve teed off the 15mm to the hob - I wouldn't have done that. Id have teed off the 28 to the hob and left that final 15mm run to the boiler unimpinged.

I hear you about the hob. If need be I'll change it. But even with the hob disconnected from the supply it didn't change the readings I got for the boiler.
 
Was the 21.5 at the meter with the boiler on max or just with the hob on.
And as everyone elce is saying dont have the hob and boiler both of the same section of 15mm pipe.
 
Was the 21.5 at the meter with the boiler on max or just with the hob on?
And as everyone elce is saying dont have the hob and boiler both of the same section of 15mm pipe.
 
Where can I get these compression test points???? I've searched but can't find them

15mm or 22mm to 1/2 t and then reducing bush from 1/2 to 1/8th
 
Status
Not open for further replies.

Similar plumbing topics

Thank you for the replies. I had another...
Replies
4
Views
834
Just do the same action again. Pot at Mac...
Replies
9
Views
1K
Absolute cock & bull from SGN, think about...
Replies
8
Views
2K
Di do not know much about this heating stuff...
Replies
16
Views
2K
What the easiest way to find why my boiler is...
Replies
0
Views
522
Back
Top