Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Low gas pressure in the Gas Engineers Forum area at Plumbers Forums

Status
Not open for further replies.
Where are you testing the pressure at the boiler? If the gas valve Vaillant say upto 3.5 mb can be lost from boiler iso to gas valve test point. I alway fit one right under boiler so I know exactly what my pipe is loosing.
 
Where are you testing the pressure at the boiler? If the gas valve Vaillant say upto 3.5 mb can be lost from boiler iso to gas valve test point. I alway fit one right under boiler so I know exactly what my pipe is loosing.

Still doesn't account for 1mb drop.. 5.5mbar it dropped in total.. so 1 from meter to boiler, 3.5 from ISO at boiler to inlet on gas valve leaves another 1mbar unaccounted for
 
Still doesn't account for 1mb drop.. 5.5mbar it dropped in total.. so 1 from meter to boiler, 3.5 from ISO at boiler to inlet on gas valve leaves another 1mbar unaccounted for

Have you checked your pockets?
 
Still doesn't account for 1mb drop.. 5.5mbar it dropped in total.. so 1 from meter to boiler, 3.5 from ISO at boiler to inlet on gas valve leaves another 1mbar unaccounted for

Have you checked your pockets?
 
Still doesn't account for 1mb drop.. 5.5mbar it dropped in total.. so 1 from meter to boiler, 3.5 from ISO at boiler to inlet on gas valve leaves another 1mbar unaccounted for

No but your pipework may not be loosing as much as you initially thought.
 
Still doesn't account for 1mb drop.. 5.5mbar it dropped in total.. so 1 from meter to boiler, 3.5 from ISO at boiler to inlet on gas valve leaves another 1mbar unaccounted for

No but your pipework may not be loosing as much as you initially thought.
 
No but your pipework may not be loosing as much as you initially thought.

Very true. Dunno wether to blast pipework with a compressor to try clear any blockages or just do a new run. Going round tomorrow to check the gas valve and ISO valve. Will see what they say.
 
Where are you testing the pressure at the boiler? If the gas valve Vaillant say upto 3.5 mb can be lost from boiler iso to gas valve test point. I alway fit one right under boiler so I know exactly what my pipe is loosing.

sorry but i disagree the hob wouldnt be going out due to 1 mbar, also ive never found anything near what mis say for gas valve restriction normally around 0.5-1 mbar
 
sorry but i disagree the hob wouldnt be going out due to 1 mbar, also ive never found anything near what mis say for gas valve restriction normally around 0.5-1 mbar

Worcesters are pretty spot on at 1.5 loss from ISO to valve, plus the 1 from meter to boiler..
 
sorry but i disagree the hob wouldnt be going out due to 1 mbar, also ive never found anything near what mis say for gas valve restriction normally around 0.5-1 mbar

To be honest I've never had 3.5 but have had 2 or so. Your right about cooker too I've had cookers lower than 15 not go out. Sounds like blockage to me and possibly more than 1.
 
sorry but i disagree the hob wouldnt be going out due to 1 mbar, also ive never found anything near what mis say for gas valve restriction normally around 0.5-1 mbar

Shaun would you reckon blasting it with a compressor is worth doing? I think the guy doesn't want pipework going around his house
 
Shaun would you reckon blasting it with a compressor is worth doing? I think the guy doesn't want pipework going around his house

I would install a test nipple below boiler least you know then if it's the boiler or Pipework
 
But if it's slow to react, when the boiler fires up the WP at the meter drops for a second and the Hob goes out

Think it's steady and not just on start up
 
That special soumds like a dicky hob. Cut a test nipple just underneath the ISO and re test.

I've ID'd the hob. But still getting 5.5mb drop from meter to boiler inlet after disconnecting the hob from the supply. To be honest I'm not really worried about the hob, they can just buy a new one. But I need to sort the pressure issue.

So it's either try and clear the blockage, if there is one, or do a complete new run.

Just toying wether to get a compressor to blow out any blockages :/
 
Vaillant reckons the boiler needs 28mm from the meter... gonna calculate it properly when I get home as forgotten how to do it :/
 
Vaillant reckons the boiler needs 28mm from the meter... gonna calculate it properly when I get home as forgotten how to do it :/

What's your total length and how many elbows ?
 
Let's say 6m, accessible elbows = 10
 
Status
Not open for further replies.

Similar plumbing topics

Thank you for the replies. I had another...
Replies
4
Views
834
Just do the same action again. Pot at Mac...
Replies
9
Views
1K
Absolute cock & bull from SGN, think about...
Replies
8
Views
2K
Di do not know much about this heating stuff...
Replies
16
Views
2K
What the easiest way to find why my boiler is...
Replies
0
Views
522
Back
Top