Where are you testing the pressure at the boiler? If the gas valve Vaillant say upto 3.5 mb can be lost from boiler iso to gas valve test point. I alway fit one right under boiler so I know exactly what my pipe is loosing.
Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws
Discuss Low gas pressure in the Gas Engineers Forum area at Plumbers Forums
Where are you testing the pressure at the boiler? If the gas valve Vaillant say upto 3.5 mb can be lost from boiler iso to gas valve test point. I alway fit one right under boiler so I know exactly what my pipe is loosing.
Still doesn't account for 1mb drop.. 5.5mbar it dropped in total.. so 1 from meter to boiler, 3.5 from ISO at boiler to inlet on gas valve leaves another 1mbar unaccounted for
Still doesn't account for 1mb drop.. 5.5mbar it dropped in total.. so 1 from meter to boiler, 3.5 from ISO at boiler to inlet on gas valve leaves another 1mbar unaccounted for
Have you checked your pockets?
Still doesn't account for 1mb drop.. 5.5mbar it dropped in total.. so 1 from meter to boiler, 3.5 from ISO at boiler to inlet on gas valve leaves another 1mbar unaccounted for
Still doesn't account for 1mb drop.. 5.5mbar it dropped in total.. so 1 from meter to boiler, 3.5 from ISO at boiler to inlet on gas valve leaves another 1mbar unaccounted for
No but your pipework may not be loosing as much as you initially thought.
Where are you testing the pressure at the boiler? If the gas valve Vaillant say upto 3.5 mb can be lost from boiler iso to gas valve test point. I alway fit one right under boiler so I know exactly what my pipe is loosing.
Slow reacting regulator when the boiler fires up?
sorry but i disagree the hob wouldnt be going out due to 1 mbar, also ive never found anything near what mis say for gas valve restriction normally around 0.5-1 mbar
sorry but i disagree the hob wouldnt be going out due to 1 mbar, also ive never found anything near what mis say for gas valve restriction normally around 0.5-1 mbar
sorry but i disagree the hob wouldnt be going out due to 1 mbar, also ive never found anything near what mis say for gas valve restriction normally around 0.5-1 mbar
Still getting same pressure loss after 10 mins on max rate
Shaun would you reckon blasting it with a compressor is worth doing? I think the guy doesn't want pipework going around his house
But if it's slow to react, when the boiler fires up the WP at the meter drops for a second and the Hob goes out
But if it's slow to react, when the boiler fires up the WP at the meter drops for a second and the Hob goes out
But if it's slow to react, when the boiler fires up the WP at the meter drops for a second and the Hob goes out
The hob only goes out on simmer.
The hob only goes out on simmer.
That special soumds like a dicky hob. Cut a test nipple just underneath the ISO and re test.
Vaillant reckons the boiler needs 28mm from the meter... gonna calculate it properly when I get home as forgotten how to do it :/