I had my boiler and tank replaced last year but since turning off the central heating this year, we noticed the radiators were still getting hot. I thought it might be the MP valve as when I disconnected the valve electrically - the rads still heated up so the valve was passing.
I just replaced the old Randall wiring centre with a new honeywell style one suitable for the Sundial Y Plan. I removed the appropriate links and connected everything as per colours indicated and double checked with the honeywell wiring diagram.
I currently am only using hot water so have disconnected the existing MP valve electrically and connected a new one electrically but not physically so I can watch the valve move before fitting to ensure its doing what it should - well its not!!!!
- When CH is selected, the valve moves to CH only and stays there regardless of whether the thermostat is activated or not
- When HW is selected, the valve also moves to CH only but when cylinder stat setting is increased - to demand more heat, it switches to the mid position!
- When CH and HW are selected, it sits in the mid position
- When both CH and HW are turned off, the valve goes to CH only - but this is because it always ends in the mid position and is driven further as normal
Pump/boiler start up correctly and cut in and out when the appropriate thermostat is activated
Any help would be really appreciated - stayed up till 2am looking at this yest!!!
Equipment fitted is:
Worcester greenstar ri boiler (1yr old)
Danfoss HSA3 MP Valve (new)
Drayton lifestyle LP522 Pogrammmer (1 yr old
Honywell wiring centre (new)
Honeywell cylinderstat and roomstat (1 yr old)
Grundfoss pump (1 yr old)
I had my boiler and tank replaced last year but since turning off the central heating this year, we noticed the radiators were still getting hot. I thought it might be the MP valve as when I disconnected the valve electrically - the rads still heated up so the valve was passing.
I just replaced the old Randall wiring centre with a new honeywell style one suitable for the Sundial Y Plan. I removed the appropriate links and connected everything as per colours indicated and double checked with the honeywell wiring diagram.
I currently am only using hot water so have disconnected the existing MP valve electrically and connected a new one electrically but not physically so I can watch the valve move before fitting to ensure its doing what it should - well its not!!!!
- When CH is selected, the valve moves to CH only and stays there regardless of whether the thermostat is activated or not
- When HW is selected, the valve also moves to CH only but when cylinder stat setting is increased - to demand more heat, it switches to the mid position!
- When CH and HW are selected, it sits in the mid position
- When both CH and HW are turned off, the valve goes to CH only - but this is because it always ends in the mid position and is driven further as normal
Pump/boiler start up correctly and cut in and out when the appropriate thermostat is activated
Any help would be really appreciated - stayed up till 2am looking at this yest!!!
Equipment fitted is:
Worcester greenstar ri boiler (1yr old)
Danfoss HSA3 MP Valve (new)
Drayton lifestyle LP522 Pogrammmer (1 yr old
Honywell wiring centre (new)
Honeywell cylinderstat and roomstat (1 yr old)
Grundfoss pump (1 yr old)