N
nzmanc
When I call for CH the boiler does not fire up. HW is fine and when on all the rads upstairs get hot. Its an S plan system with the pump on the return. The pipes are hot past the valve that should control the CH. Would I be right in thinking this valve is passing and not talking to the boiler and so needs replacing. Im also thinking there may be an airlock on the drops to the lower rads hence why they arent heating. The system is microbore and was switched off for a couple of months. any thoughts?