I have to disagree Gray0689 I asked the very same question years ago at OFTEC and I was told it should be fitted externally for the reason I mentioned.The tiger loop is fine inside boiler house
We recommend uHeat for Underfloor Heating Systems, and The Wetroom Store for all things bathrooms and wetrooms. They provide discounts for forum members.
Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws
I have to disagree Gray0689 I asked the very same question years ago at OFTEC and I was told it should be fitted externally for the reason I mentioned.The tiger loop is fine inside boiler house
I have to disagree Gray0689 I asked the very same question years ago at OFTEC and I was told it should be fitted externally for the reason I mentioned.
Tigerloop must be fitted EXTERNALLY IE OUTSIDE as it can vent vapour, which must not be sucked up by the boiler
What a complete mess!
COWBOY ALERT!
COWBOY ALERT!
COWBOY ALERT!
Guy is DEFNINTELY not registered, and look incompetent. If it hasn't been installed properly it could also be dangerous.
Go to Oil Firing Technical Association - registered professionals for the the oil heating and cooking industry - OFTEC, Kesgrave, Ipswich and find a technician in your area to do the job properly.
Tigerloop Original - for external mounting only. This device is not permitted for indoor installation as it vents contaminated air into its surrounding environment, this could create explosion or health hazards in confined spaces and therefore must be fitted on the outside wall of any premises. For situation where the boiler is not mounted to the perimeter wall, use a Tigerloop Bio
Wrong - quote from the Tigerloop instructions:
Would be better in a sleeved pipe (especially the underground part).
- Yeah it is the sleeved copper pipe that he used : but bits where the sleeve has been stripped back for a joint for example - is there something to cover these (or indeed compression valves) or should I no worry?You can purchase sleeved copper pipe just for the purpose. (10mm pipe sleeved with plastic to an overall diameter of around 15mm).
We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.