Pressure testing 63mm gas pipe

So reading the pipes testing procedure for gas, it says to reduce temperature effects the trench must be backfilled. That is surprising
 
I contacted another department today a d all they could tell me in that area it is all low pressure installations which will supply a MOP of 19 to 21mb. Does this help?
 
I see in this table it is below 100mb so MOP x 2.5

Screenshot_20181218-230626_Chrome.jpg
 
You need to find out the Mains pressure before the Governor that controls your installation pressure. Cadent will tell you what the supply pressure is in that area. If you get that, I can look in IGE/UP/1 and tell you the pressure you need.
 
Which ever is greater so mop might be 21mbar so 52mbar test

But mip could be 75 mbar so 82 mbar test

So mip is your testing pressure
 
I have talked to 4 people now and they don't know any figures just that the pressure in the mains gas pipe in the road is low pressure. Very frustrating
 
Must be a nightmare.

To be honest, Cadent would of had it but it is not there area. It is SGN.

I have found this info though...

Going from that info it is what you have suggested and 75mb for low

Screenshot_20181219-093110_Chrome.jpg
 