A
anotherdiyjob
Anyone had this:?
'Y' plan single feed/return potterton boiler(fairly recent), 3-port motorised valve(recent), sunvic programmer (recent), pump (very recent), hw cyl (fairly recent).
Original symptoms: downstairs rads cold, upstairs hottish, hw supply hottish.
Powerflush was recommended, company contracted (poor job done, with the result of burned out pump, leaking joints, broken-off rad valve stems, damaged pump isolator valves, etc). Fault traced to boiler cold feed blockage, cleaned out and chemicals added. Pump replaced. Company did not return to flush/check/set/test after a couple of weeks. Pumping over (pump was left on high), was told 'It will do that for a while'.
Inmate (tenant!) complained heating only came on with hot water, and was sporadic. Sunvic programmer was not sending command to open 3-way to rads. (internal relay replaced (couldn't geta programmer at 2a.m.!). heating restored, but severe pump-over evident (in all modes).
system was perfect before initial problems. pump is placed after vent(22mm) & feed(15mm), and goes straight to 3-way diverter (pumping INTO valve). even with pump on lowest speed, pump-over occurs. All rads get hot, as does hwcyl.
Could pump be too powerful?
Only other thing I can think of is a 15mm isolator (ball type) was fitted on the cold feed from the header/expansion tank. Possibly causing a resriction?
HELP!
thanking you in anticipation.
'Y' plan single feed/return potterton boiler(fairly recent), 3-port motorised valve(recent), sunvic programmer (recent), pump (very recent), hw cyl (fairly recent).
Original symptoms: downstairs rads cold, upstairs hottish, hw supply hottish.
Powerflush was recommended, company contracted (poor job done, with the result of burned out pump, leaking joints, broken-off rad valve stems, damaged pump isolator valves, etc). Fault traced to boiler cold feed blockage, cleaned out and chemicals added. Pump replaced. Company did not return to flush/check/set/test after a couple of weeks. Pumping over (pump was left on high), was told 'It will do that for a while'.
Inmate (tenant!) complained heating only came on with hot water, and was sporadic. Sunvic programmer was not sending command to open 3-way to rads. (internal relay replaced (couldn't geta programmer at 2a.m.!). heating restored, but severe pump-over evident (in all modes).
system was perfect before initial problems. pump is placed after vent(22mm) & feed(15mm), and goes straight to 3-way diverter (pumping INTO valve). even with pump on lowest speed, pump-over occurs. All rads get hot, as does hwcyl.
Could pump be too powerful?
Only other thing I can think of is a 15mm isolator (ball type) was fitted on the cold feed from the header/expansion tank. Possibly causing a resriction?
HELP!
thanking you in anticipation.