Rate of heating in a living room? | UK Plumbers Forums | Plumbers Forums
  • Welcome to PlumbersTalk.net

    Welcome to Plumbers' Talk | The new domain for UKPF / Plumbers Forums. Login with your existing details they should all work fine. Please checkout the PT Updates Forum

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

American Visitor?

Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Rate of heating in a living room? in the UK Plumbers Forums area at Plumbers Forums

Messages
64
If a radiator has been correctly sized for a room and the boiler is adequate and fully functioning, at what rate of C/Hour would you want a living room to be able to heat up at?

Thanks.
 
Should be able to heat the room up in under 30 mins
 
So if it's heating up the room at a rate of between 2.5C - 3.0C / hour, this is too slow? I think it's too slow, but wondering what opinions are.

This is with heating system at ~60C at the boiler, and the thermostatic valve radiator turned up full.
 
So if it's heating up the room at a rate of between 2.5C - 3.0C / hour, this is too slow? I think it's too slow, but wondering what opinions are.

This is with heating system at ~60C at the boiler, and the thermostatic valve radiator turned up full.

rad sounds undersized
 
What’s your room size height etc
Windows
Outside walls etc
 
You say you have a flow temperature of 60°c? Is this a condensing boiler. If using delta t 50 rads they won't be working anywhere near full output. The power required is the output needed at a design outside temperature to design end internal temperature to bring the room upto temperature and keep it there, bare in mind the air change rate, so a lot of the power is required to re heat and maintain. With the system designed and executed properly you should be nice and toasty in about 30 minutes as Shaun says above.
 
You say you have a flow temperature of 60°c? Is this a condensing boiler.
It's a WB Combi 30i boiler with the rad below:
I believe BTU measurements on that site are based on delta t 50 C.

I went looking for a tape measure there so I wouldn't be estimating the measurements. Measurements are:

Room size: 3.16 m X 2.94 m X 2.66 m (Height)
One window (Single glazed): 0.80 m x 1.53 m

Only one exterior wall which is cavity wall insulated. Mid terraced house.
 
From -10 to 21dc 14 mins so something isn’t right

does the rad get hot hot eg 60dc ish
 

Attachments

  • CC6FCB06-AB75-4958-B241-F9C46CBB87C9.png
    CC6FCB06-AB75-4958-B241-F9C46CBB87C9.png
    123 KB · Views: 36
I have pointed a contact free thermometer pointed very close to the rad and it gives a temp of ~58 C.

I would say the specs that the manufacturer has claimed are over zealous and would estimate it to emit around 1.5-1.8 kw (max)as it’s basically a single panel rad
 
I would say the specs that the manufacturer has claimed are over zealous and would estimate it to emit around 1.5-1.8 kw (max)as it’s basically a single panel rad
Thanks.

I suppose there's no way to guesstimate what BTU size I should really be looking for for this type of rad on this site? That is, using their BTU measurements.

It will get the room up to 21C/22C but it takes hours to do so.

What kW would you normally want to get from a radiator?
 
Last edited:
That’s a 1.2x600 double panel double convector eg k2
 

Attachments

  • ACAD3DB9-9231-45CF-9BB4-903DA2108B63.png
    ACAD3DB9-9231-45CF-9BB4-903DA2108B63.png
    83.6 KB · Views: 34
Last edited:
Unfortunately I don't have a plumbing background, so I'm unsure what exactly this means.

I understand that k2 is a type of rad. Do you mean if using a double panel 1.2m x 600mm K2 rad this would give an average BTU output of 7401 BTU?

The current rad type which I have would probably need to be a lot bigger to heat up the room in 30 minutes since it's heating the room at ~ 2.5C - 3.0C / hour.
 
Unfortunately I don't have a plumbing background, so I'm unsure what exactly this means.

I understand that k2 is a type of rad. Do you mean if using a double panel 1.2m x 600mm K2 rad this would give an average BTU output of 7401 BTU?

The current rad type which I have would probably need to be a lot bigger to heat up the room in 30 minutes since it's heating the room at ~ 2.5C - 3.0C / hour.

correct

or another rad installed in the same room eg two rads
 
So essentially if I wanted to get this make/model of rad to heat the room up in a reasonable amount of time (and I only wanted one rad as it's a small room) the rad may need to be in the region of twice the output size of the one currently installed?
Also because you are running with a boiler temp of 60C then you will only be getting ~ 65% of a 50 deg rad output or ~ 4810 BTU (1.4kw).
 
It looks like their only larger rad of this style is:
which has 9163 BTU as opposed to the 8218 BTU for the one which I have. I'd guess this won't make a huge difference in getting the room warmed in 30 minutes, so perhaps I might look at some other radiator design.

Also because you are running with a boiler temp of 60C then you will only be getting ~ 65% of a 50 deg rad output or ~ 4810 BTU (1.4kw).
Should the boiler temp be run at a different temperature? I've set the WB combi to the recommended "e" setting and this is usually about 60C.
 
It looks like their only larger rad of this style is:
which has 9163 BTU as opposed to the 8218 BTU for the one which I have. I'd guess this won't make a huge difference in getting the room warmed in 30 minutes, so perhaps I might look at some other radiator design.


Should the boiler temp be run at a different temperature? I've set the WB combi to the recommended "e" setting and this is usually about 60C.
If you increased the boiler temp to 75C and with a radiator deltaT of 15C, you would then almost have a 50 deg (47.5) rad again or 94%% output but the boiler is then running with a return temp of 60C which is very uneconomic, if you run with a delta T of 20c you are down to 87% output, all rads should really IMO be oversized by a factor of at least 1.5 to allow for condensing boilers which run most efficiently with return temperatures of 50C or less.
 
It looks like their only larger rad of this style is:
which has 9163 BTU as opposed to the 8218 BTU for the one which I have. I'd guess this won't make a huge difference in getting the room warmed in 30 minutes, so perhaps I might look at some other radiator design.


Should the boiler temp be run at a different temperature? I've set the WB combi to the recommended "e" setting and this is usually about 60C.

Tbh I wouldn’t trust there output as your having problems with the lack of heat
 
Can I just add modern condensing boilers are looking for a DT of 20°c. If you were to adjust the flow temperature to 75°c and keep the DT at 15°c then the mean radiator temperature does increase and increase its output but you're then running a return too high for condensing and this is not desirable for efficiency or the life expectancy of the boiler.
To maximise condensing you really want a lower temperature system but as I said above the size of the emitters will need to be reconsidered.
 
I suppose there are two calculations that the heating engineer should do when sizing radiators, one is the calculation for the heat loss and the other for the correction factor to apply to a 50 deg rad. A required return temp of 40C with deltaT of 20C will result in a 30 deg rad based on a required room temp of 20C or a 27 deg rad based on a more realistic required temp of 23C, this will result respectively in 51.5% output and a correction factor of 1.94 or 44.9% output with a correction factor of 2.22, so as suggested with the above slow warm up problem, maybe install another rad of the same size?. It would be interesting if the flow and return temps were actually measured in the above case as the "58C" measurement implies a delta T of 4C (boiler temp 60C) which is unlikely IMO.

Maybe the new norm should be 30 degree Rads, it wasn't so mighty long ago that the 60 degree Rads were.
 
Last edited:
The radiator in question has a BTU output according to the manufacturer of 8218 BTU at delta 50 C.
Room size: 3.16 m X 2.94 m X 2.66 m (Height)
One window (Single glazed): 0.80 m x 1.53 m

Would anyone care to suggest any other makes/models of vertical radiators that I could take a look at that might heat the room in 30 minutes or so with just one radiator?

That is, radiators which are 1800 mm max x 560 mm max.
[automerge]1607263215[/automerge]
I found this interesting:

Original rad: 1800 X 470mm Vertical 3 Column Radiator. BTU: 8218

Rad B: 1800 H X 490 W 3 Column Vertical Radiator. BTU: 5664 at delta T 50 C

Rad C: 3 Column Vertical Radiator 1800x470mm . BTU: 7463 at delta 50 C

These are broadly similar rads in terms of height, width, style and number of columns. Presumably with 3-column traditional styled rads of 1800mm in height and the same width should give a broaly similar output? Presumably manufacturer's aren't able to produce a much larger BTU output for a broadly similar product compared to others?

I suppose the 5664 BTU figure is probably the type of figure one should assume this type of rad would be capable of outputting?
 
Last edited:
This site has numerous posts re problems with vertical rads, some have to be installed in a certain way as they have a baffle to get the water circulating properly and apparently sometimes this isn't pointed out in the installation instructions. I would suggest taking numerous temperature readings on the columns and make a little sketch with the temps noted on it, as a very quick check you might just measure the temperatures at the flow and return connections, if these are only a few degrees apart then IMO you have a problem, just feeling the rad all over even should tell a lot.
 
New posts

Similar plumbing topics

  • Question
If it gets fully hot with other rads off, the...
Replies
1
Views
674
  • Question
Did what gmartine recommended work?
Replies
2
Views
622
  • Question
I wanted to bring this one to conclusion. My...
2
Replies
36
Views
3K
  • Question
There are 7 manifolds total. I”m no expert...
Replies
2
Views
763
  • Question
Its a very ingenious but devilishly cunning...
2
Replies
25
Views
3K
Back
Top