Hi Guys, just a quick one.... i was comissioning a new boiler the other day (ideal logic combi 30) i put my fga on it and ran at full rate and was getting a ratio of 0.009!! co2 reading was 9.32% and gas rate/working pressures were fine. Looked at mi's and they stated that 0.004 was the target. Now this being a brand new boier should i need to be fiddleing around with it?
I went on a wb cdi course earlier in the year and the fella said that when doing a fga check he would always go by the co2 reading as this is the gas emissions and as long as this is below 11% there would be no need to take any further action. What's your take on this?
I went on a wb cdi course earlier in the year and the fella said that when doing a fga check he would always go by the co2 reading as this is the gas emissions and as long as this is below 11% there would be no need to take any further action. What's your take on this?