Hi, I’m a Rayburn engineer & I’m clutching at straws with a problematic cooker!
I got called to a Customers house as their previous engineer has now washed his hands of the job … the fault is the cooker side will go through it’s prevent sequence, the burner will fire up but as soon as the transformer turns off the burnt goes out and goes to lockout.
(Boiler side works fine).

Usually for me this points to the PEC or the control box, both have been changed and the problem still happens so I changed both the finder relays (1 is for the oil pump and other is for ignition) again no joy.
I called Rayburn tech but they just referred me to the manual and to use the fault finding flow chart which isn’t helping solve the issue.

I’ve confirmed both coils are opening and do not have undervoltage and the I can see both cool bodies have been replaced recently to try and remedy the issue with no success!

My next step is to test the PEC lead for a break and/or any other wires in the control panel but it certainly seems like an electrics issue, the burnt has been fired up so much now I’ve had to replace the transformer as it was starting to melt but again the problems still exists.

I’m open to any advice or suggestions?

Thanks
Ryan
 
Use your multimeter and measure the microamps coming back from the cell. Might be not be within tolerance. Could be the control box mounting plate as well. I assume it's an electrical fault like you.
 
Use your multimeter and measure the microamps coming back from the cell. Might be not be within tolerance. Could be the control box mounting plate as well. I assume it's an electrical fault like you.
 
Use your multimeter and measure the microamps coming back from the cell. Might be not be within tolerance. Could be the control box mounting plate as well. I assume it's an electrical fault like you.
I replaced the cell & control box with the functioning one in the boiler side with no success so I think I’m down to a loose wire or potentially a bad base fixing like you suggest …. 🥵
 

Similar plumbing topics

  • Question
That's October last year. What are they today?
Replies
4
Views
1K
  • Question
Just wanted to say thanks to yourself and...
Replies
19
Views
2K
How are you getting on, anything to update?
2 3 4
Replies
98
Views
14K
  • Question
Yes it was the non return valve on the bottom...
Replies
18
Views
8K
  • Locked
Hi I am a newbie and hate to join and ask for...
Replies
0
Views
1K
Back
Top