Right I will just tell you why not to use plastic on secondary returns.....
This came from a big chief at Hep20 owned by Wavin......we kept going to water leaks in a nursing home when the pipe had failed, so lads on call just banged a meter with a couple of sockets job done, but sadly, it kept happening, I got called out and noticed it was only the secondary return, every other pipe installed in the same place and the same time, same materials etc was ok......
i made a call, and it basically comes down to the pipes composition, it is not continually rated for heat 24/7 like Mike pointed out, why? Because of the memory effect it needs to cool down, he quoted for every hour on, it should be off an hour, obviously not intermittently, but if on 12 hours it should be off 12 hours in total......as the plastic heats it changes state, and only relaxes and goes back to the state when cool, if it does not get back to its original state, it becomes more brittle and will fail eventually.....just like bending a shatter proof ruler, it won't break straight away, bit it will turn white, where the stress is, then fail at that point, if it is subjected to more stress over time.
As some have pointed out, in domestic applications where the pump is timed it should not be a problem, unless its left on constant......be warned insurance companies are getting wise to water damaged claims, we had the one in a new build, loss adjuster with the aid of his plumber, pointed out it was not fit for purpose, they refused to pay out!