I know its replying to my own thread, again, but am I missing a boiler bypass here? if all four electronic zone valves are shut, I see no route to discharge the residual heat. Or am I missing something obvious as a novice?
EDIT: found the following in the installation guide for the boilers:
"However, if the system employs thermostatic radiator valves on all radiators, or two port valves, then a bypass circuit must be fitted with an automatic bypass valve to ensure a flow of water should all valves be in the closed position."
AND
"Systems incorporating zone valves which could completely cut off the flow through the system must also include a bypass."
As I have TRVs on all rads, and zone valves which could cut off the flow in all directions, Im assuming this applies to me and a bypass needs to be fitted?
EDIT: found the following in the installation guide for the boilers:
"However, if the system employs thermostatic radiator valves on all radiators, or two port valves, then a bypass circuit must be fitted with an automatic bypass valve to ensure a flow of water should all valves be in the closed position."
AND
"Systems incorporating zone valves which could completely cut off the flow through the system must also include a bypass."
As I have TRVs on all rads, and zone valves which could cut off the flow in all directions, Im assuming this applies to me and a bypass needs to be fitted?