Perhaps a few more of you should also pay heed to what he has to say cos from where I am sitting there are some big miss understandings on boiler / system load sizing.He taught me everything I know Paul, & then some !!!
For my part I would just ask you to have a think about what happens to the boiler efficiency during over half of the year when no heating is required i.e. just the hot water, if you are going to add the heating load to the cylinder coil size?
The whole idea of making the cylinder coils so large is to heat it as quickly as possible, with the water coming back to the condensing boiler as cool as possible & without it continually cycling on & off (all in Part L). To aid this there is a requirement that the hot water is independently timed to allow the hot water to be generated first & then once satisfied (& if required), the heating can be switched on.
I see no reason to add any allowance for HW to the boiler size but if so it should be limited to between 2 - 3 kWs as per heating design guide but just think the boiler selected is normally larger than the required heating load anyways.