Unvented cylinder in loft - terminating tundish | UK Plumbers Forums | Plumbers Forums
  • Welcome to PlumbersTalk.net

    Welcome to Plumbers' Talk | The new domain for UKPF / Plumbers Forums. Login with your existing details they should all work fine. Please checkout the PT Updates Forum

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

American Visitor?

Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Unvented cylinder in loft - terminating tundish in the UK Plumbers Forums area at Plumbers Forums

Not sure what else to add. It's an unvented cylinder install in the loft of a two bathroom extended semi-detached. I've only ever put them in cylinder cupboards, garages and utility rooms.

32mm pipe gives you plenty of options with regard to distance and bends. If not you are looking at doing it in copper tube for a neater look.
 
Ill need to check with client for load bearing walls to reposition it, a shorter run in copper does seem a better and neater option.
[automerge]1581964112[/automerge]
32mm pipe gives you plenty of options with regard to distance and bends. If not you are looking at doing it in copper tube for a neater look.

I've just found a figure for the fall required (1:200), is that right?
 
Last edited:
Only other way is to pump it but best part of 500 smacks

cant you get into a drain somewhere? down into the airing cupboard and into the bathroom or any soil vents in the loft ?
 
If you have access to the stack then why not? That's a good solution. Alternatively you can take the D2 outside and down to the ground (must terminate within 100mm of ground level) and put a little protective cage around the end of the pipe as per regs. Obviously depending on where this is on the building it can look ugly but at the side or around the back I have found most customers don't mind the pipe showing. This also allows you to fully comply with the "Discharge visible at two points" part of the regs.
 

Similar plumbing topics

  • Question
Need to phone up local building control and...
Replies
4
Views
497
Replies
2
Views
711
  • Question
Removed now
Replies
84
Views
7K
  • Question
Having a Viessmann 100W using the 4 pipe...
Replies
3
Views
597
A
  • Question
Nice spot exedon2! Eagle eyes. OP - yes your...
Replies
4
Views
2K
Back
Top