Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Unvented cylinder size in the UK Plumbers Forums area at Plumbers Forums

Messages
97
200/210 or 250l indirect unvented cylinder...

Pros and cons of both please guys, whats the thinking??
Better to go bigger, or are there other considerations to be thought of....?
 
Tbh i'd go off local recommendations from people who have actually used someone.
Agreed. Alternatively, if that doesn't work, try the cylinder manufacturer's website. They'll usually list several 'approved installers' for your area. They'll have done the manufacturer's product-specific training and you may get a longer warranty if you use them.
 
Is that INC VAT and you supplying all the materials and sourcing them? Or they sorting materials too.
Thats purely the labour content.inc vat. I have the cylinder, they say to supply pipe and fittings. Plus 1 zone valve.
Change y to s plan.
Move mag filter, as apparently its only on heating return and doing nowt for the boiler.
Raise f+e tank in loft.
Fit cylinder in loft on platform ive built.
Pipework to be run up new airing cupboard wall. Its a blank canvas in my book...

Am i so out of touch with life in 23!!?
 
Also I would recommended sealing the system as the cylinder is in the loft high chance of pumping over
 
3 days for 1 man?
NO, no soil vent, but there are easy options for discharge i would think...

Yes or 4 if it’s a pain discharge has to be copper or high temp plastic and if over x m it has to be 28mm it can’t be overflow tube
 
I would as your having the cylinder in the loft better heat up times customers report and not open to atmosphere so better water quality if flushed
 
Why high chance of what pumping over??

You haven’t much head from the top of the cylinder coil and bottom of the f and e tank at present you have around 2.4m ish with a cylinder in the loft maybe 1-1.5 m max
 
Yes you want a min of 2m above the coil of the cylinder to the bottom of the f and e tank
 
Think of your current height and coil height bet that’s over 2m
 

Similar plumbing topics

  • Question
Having a Viessmann 100W using the 4 pipe...
Replies
3
Views
596
Replies
1
Views
966
  • Question
Hi All, looking for some advice. I have...
Replies
0
Views
996
  • Question
And it's fixed! Had someone move the EV from...
2
Replies
27
Views
3K
H
  • Question
I use UK Exchangers ltd. I’ve fitted both...
Replies
8
Views
896
Back
Top