I'm looking to replace my water supply. I will be digging the trench on my side myself. I have all the safe dig plans etc and found the guide on the southern water website:
Slightly confused by the 750mm minimum from the outside wall. Is this an actual thing? Every stopcock I have ever seen has been secured to the wall in some way. My wall construction is solid block-work with insulated stud wall which comes to 342.5mm thick all in. This means the pipe would come up in the middle of the floor.
2nd question is if I use 32mm MDPE the minimum bend radius would be 480mm. Would I be allowed to use a compression elbow like the one in this link within the pipe lagging part after the footings so that it can come up closer to the internal wall?
Below Ground Elbow
Slightly confused by the 750mm minimum from the outside wall. Is this an actual thing? Every stopcock I have ever seen has been secured to the wall in some way. My wall construction is solid block-work with insulated stud wall which comes to 342.5mm thick all in. This means the pipe would come up in the middle of the floor.
2nd question is if I use 32mm MDPE the minimum bend radius would be 480mm. Would I be allowed to use a compression elbow like the one in this link within the pipe lagging part after the footings so that it can come up closer to the internal wall?
Below Ground Elbow