Wiring a y-plan system for a worcester greenstar 28he without capacitor | Plumbing Jobs | The Job-board | Plumbers Forums
  • Welcome to PlumbersTalk.net

    Welcome to Plumbers' Talk | The new domain for UKPF / Plumbers Forums. Login with your existing details they should all work fine. Please checkout the PT Updates Forum

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

American Visitor?

Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Wiring a y-plan system for a worcester greenstar 28he without capacitor in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.

Nas

Plumbers Arms member
Plumber
Gas Engineer
Messages
133
Is there a way of wiring this boiler to a y-pan system so it does not require a capacitor on the switched live. I have wired it up but the heating will not switch off. After checking everything Im assuming it's because I've not got the capacitor in the circuit.

Thanks in advance
 
You could use a relay or contactor to do the switching but a capacitor would be cheaper.
 
how old is this boiler not used a relay for years usually normal wiring for y plan
have you checked on honeywell website for a diagram
 
Its about 6 years old. Just been relocated.
 
I have never fitted a capacitor on these double check the wiring see what voltage you get on orange wire with everything off.
 
The problem with Y plan is that you get a potential difference between orange and neutral when the valve is off.
This is sometimes sufficient to operate some boilers when it is connected to the SL.
Doesn't happen with S plan.
 
Turns out the boiler had the older version of the PCB. New pcb has resolved the issue
 
Status
Not open for further replies.

Similar plumbing topics

thanks.... yes, so my diagram and wording is...
2 3
Replies
55
Views
2K
  • Question
Its a very ingenious but devilishly cunning...
2
Replies
25
Views
3K
3 hw on 4 htg on 5 perm live
Replies
1
Views
1K
Interesting idea when most people at the...
Replies
5
Views
1K
Anyway, you can always increase the boiler...
Replies
16
Views
1K
Back
Top