hi all dont know if any1 can help me the dhw keeps running hot and then goes cold and then goes hot again, i think it might be the diverter valve but not sure???
 
try a thermistor easy to change on the 350 its in front of you just above the pcb houseing
 
no divertor on 350, sounds like blocked plate heat ex. does boiler go off then come back on.
 
change both dhw thermistor and primary, but if boiler cuts out on dhw demand i think you will find the plate blocked, cheat reduce max gas rate on hot water to 8.5 mbar, this should work
 