Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Advice on heating in a new build property in the UK Plumbers Forums area at Plumbers Forums

Messages
169
Hey guys

looking for abit of advice on my heating system in a house I’ve just moved into. Last week I had to bleed a few radiators which I thought was normal but today I’ve had to go round bleeding them again and there was quite abit of air in them. How often should they need to be bleed? The down stairs toilet needed bleeding first time round but now it’s stone cold but doesnt need bleeding. What could be wrong with this? Also a few radiators are hot to touch but if I put my hand over the top it doesn’t feel like much heats coming off them and lastly for a new build property it’s costing anything from £4-6a day for gas and the heatings only on a few hours a day but doesn’t seem to reach temperature. For a new build property it seems abit excessive my old house was built In 1960ish and didn’t cost this much to run.

any help would be appreciated

thanks
 
Yes the cylinder on the top floor just outside the bedroom
tbh 15k on new builds is fine with level of insulation running 15 rads see it all the time. I know you shouldn't have to do this but if you go round all the rads make sure the lockshield valves are fully open. turn off the HW then turn both heating stats on and make sure pump is on max setting then turn all the rads off except one, run this rad for a minute or so so you know all the air in the pipwork has been cleared, go to next rad turn this one on then go back to previous and turn it off to clear next rad pipework of air. repeat this step one rad at a time till you have been round all the rads. turn system off and vent all rads and check system pressure. open all rads to max setting and run boiler with HW and both heating zones on and see if all rads get hot. if not its a balancing issue which site should sort out. had this so many times where boiler on ground floor being pumped up to top floor then back down to ground floor rads on microbore. pump setting can be sorted after you know all rads are balanced
 
Plumber came round earlier to look at the heating played with a couple of lockshields got the rads warm and then went as I suspected he would. The heating was on from 12 when he turned up and by half 4 it had gone from 15 degreees to 19 degrees so 4 degrees in 4 and a half hours. At 2pm she turned the upstairs stat off because the 2 smaller bedrooms wasn’t even warming up even with the doors closed. And all this has cost £3.50
 
Just wanted to give you guys a quick update. I’ve spoke to the site Forman and he’s getting the company that does all the insulation out to get there isn’t anything cold spots etc as the plumbers keep saying the radiators are hot it’s working fine. I’ve started writing down the times, temperatures and cost every hour of the day. I just wanted to ask if I’ve got theos the right with the boiler usage. Am I right in thinking if all my radiators add up to 8.5kw and the gas kwh is 4.23p then if the boilers running at 8.5kw it’ll be using 35p per hour?
 
No, you need to convert from gross to net. So at 4.23p /kwhr that equates to £0.40/hr. (multiply your calculation by 1.11).

Having said that, it is unusual ( in my experience) for a gas boiler to operate at full capacity for a prolonged period unless it is heating a swimming pool or the outside temp is consistently below -2 degrees C . This winter has, to date, been unusually warm - my gas bill for heat and water (in Oxon) is minimal ( £2.90 /day) for a 27kw system.

In the current market you should be paying around 2.7p per Kw (inc vat) for gas - Utility Point are around 2.45p per Kw. Gas prices are falling quite rapidly at the moment so be wary of locking into a fixed price deal
 
Yes, measure the gas rate at the meter, them convert it to KW. That will give you a snap shot in time of what the boiler has modulated to. Not sure how that would help you though.

Very unlikely, in my view, that there is anything significantly wrong with the performance of your boiler.

You would be better off spending your time looking at heat loss calculations to determine the correct sizing of the radiators and insulation of the property.
 
Last edited:
Yes the boiler goes to 00 and there’s 16 radiators in the whole house. I’ve been round and added up all the kw for the size and type of radiators and it comes to 8.7kw so we’ll in the boiler capacity
[automerge]1576444668[/automerge]
Sorry my mistake on both radiators on the top floor where the stat is there isn’t any trvs on them
16 Rads total 8.7 kw are you heating a dolls house. centralheatking
 
All radiators apart from 2 are k1’s and the other 2 are k2’s I’ve been round all of them and took the measurements then got the kw per radiator from the stelrads website which adds up to 8.7kw
I have installed loads of heating systems since 1980 until a few years ago but because of my business in plumbing and heating keep up or even ahead. Do not be fooled its a case of emporers clothes the system looks good maybe just meets modern regs etc. in reality my last gaff had 30kw over 3 floors and 14 or so rads and guess what I could turn it down ! wait till we get a real cold blast. get some more kw in or buy some electric convection heaters when they are cheap after Easter. centralheatking
 
You cannot raise the tempreture in the property to a comfortable level even after hours of running the system the boilers to small in my opinion, the rads may well be just about adequate but only if you can get enough heat into them which you are struggling to achieve . Kop
[automerge]1577567090[/automerge]
Isolate 50% of the radiators and see if you can get the downstairs up to temperature. ?
 
Last edited:
Just what I was going to say, on a cold day turn off/down one of your zones and see if the remaining zone gets up to temp then do then do the opposite and see if the other zone gets up to temp. If both zones get up to temp individually but not together you have your answer, I'd also check when your cylinder is calling for heat.
 
hey guys

6 weeks later and im still in the same situation. Had the insulation people out to check all insulation which is ok. Ive worked out the maximum gas the boiler can run on my current gas rate is 71p per hour. Over the last week or so ive been writing down every hour how much gas has been used. It ranges from 40-70p every hour even when the house is upto temperature. Even though the stats turn off it doesnt take long before their kicking back in again. During the heating times the boiler doesnt really get a break.

Ive emailed ideal technical explaining the situation hoping they might shed some light on the possible causes. I think one of the causes could be the size of the rads in the hallway and both landings. Am i right in thinking when measuring the hallway you measure the stairs as if they wasnt there ? The hallway is 5m long and 1m wide with an external front door according to the stelrad website should need a btu of 2568. Then the stair space measures 1.8m by 1m with 1 external wall and again on the stelrad website it says it needs a btu of 925 which together equals 3493. The rad in there is a stelrad k1 600 x 500 which gives out 1575 btu. This is the same on the first and second landing

Ive measured the bedrooms and the size of the rads in there they seem right but only just they seem to have put bare minumum in there

Any help would be appreciated
 
hey guys

6 weeks later and im still in the same situation. Had the insulation people out to check all insulation which is ok. Ive worked out the maximum gas the boiler can run on my current gas rate is 71p per hour. Over the last week or so ive been writing down every hour how much gas has been used. It ranges from 40-70p every hour even when the house is upto temperature. Even though the stats turn off it doesnt take long before their kicking back in again. During the heating times the boiler doesnt really get a break.

Ive emailed ideal technical explaining the situation hoping they might shed some light on the possible causes. I think one of the causes could be the size of the rads in the hallway and both landings. Am i right in thinking when measuring the hallway you measure the stairs as if they wasnt there ? The hallway is 5m long and 1m wide with an external front door according to the stelrad website should need a btu of 2568. Then the stair space measures 1.8m by 1m with 1 external wall and again on the stelrad website it says it needs a btu of 925 which together equals 3493. The rad in there is a stelrad k1 600 x 500 which gives out 1575 btu. This is the same on the first and second landing

Ive measured the bedrooms and the size of the rads in there they seem right but only just they seem to have put bare minumum in there

Any help would be appreciated
Thanks for keeping us informed, this might be the right time for you to re summarise your position as not everbody will have time to read it all from the beginning . My take on your problem is this
1. New build 2. Bare minimum heating system which does not reach your quite reasonable expectations 3 Total kw rad output 8kw. 4 boiler rarely modulates just races on to keep up
Question ..what is the boiler and it’s output in Kw Centralheatking
 
Thanks for keeping us informed, this might be the right time for you to re summarise your position as not everbody will have time to read it all from the beginning . My take on your problem is this
1. New build 2. Bare minimum heating system which does not reach your quite reasonable expectations 3 Total kw rad output 8kw. 4 boiler rarely modulates just races on to keep up
Question ..what is the boiler and it’s output in Kw Centralheatking

Thanks for the reply

The boiler is an ideal logic heat 15kw

ive been asking the plumbing company for the spec of rads boiler etc thats been requested from the builders but they ignored me and also asked the builders which he said hes laptops playing up which is a coincidence but hes ment to be coming round next week to go through it with me. Where do i stand with them putting bare minimum in which clearly isnt working?

ive also noticed pipes knockng in places when there cooling down. Whats the cause of this?
 
i havent asked them directly but i checked their meter every day same time for a week to see what they was using (naughty i know) they was using roughly £1.80-2 on the rate im on. Although there house is a 2 storey one and mines slightly bigger i cant see me using twice as much as them. Theres still 5 people living there all seem to be home at different times during the day and when i get home from work between 4-5 theres steam coming from their flu so heating must be on
 
Insulation might be OK but have you not considered draughts? Draughts will cause your house to cool down much quicker than no insulation.... Poorly fitted doors/windows, seals not fitting correctly, loft hatches not sealing, extractor fan back draughts not working etc.
 
Thanks for the reply

The boiler is an ideal logic heat 15kw

ive been asking the plumbing company for the spec of rads boiler etc thats been requested from the builders but they ignored me and also asked the builders which he said hes laptops playing up which is a coincidence but hes ment to be coming round next week to go through it with me. Where do i stand with them putting bare minimum in which clearly isnt working?

ive also noticed pipes knockng in places when there cooling down. Whats the cause of this?
15kw is a joke for your property 2x that in my opinion Chking
 
the house was air tested for draughts etc not sure if this means anything? when the heatings off the house takes a while to cool down say its 22 degrees when the heating turns off itll only go down a degree or so over the next 1-2 hours. from experience from previous houses when the stats reach temperature they keep raising to a degree or so higher as the rads keep giving abit of heat out but this doesnt seem to happen in this house itll get to 21-21.5 degrees then turn off thinking itll keep rising but it doesnt casuing it to come back on a few minutes later

how would you determine what size boiler is required?
 
the house was air tested for draughts etc not sure if this means anything? when the heatings off the house takes a while to cool down say its 22 degrees when the heating turns off itll only go down a degree or so over the next 1-2 hours. from experience from previous houses when the stats reach temperature they keep raising to a degree or so higher as the rads keep giving abit of heat out but this doesnt seem to happen in this house itll get to 21-21.5 degrees then turn off thinking itll keep rising but it doesnt casuing it to come back on a few minutes later

how would you determine what size boiler is required?
Your stats will come on and off as they’ll be TPI stats. They’ll work out how quickly a room cools down then come back on before the temperature decreases to maintain the room at that temp.
As Scottd says have you got the HW on at the same time? Ensure that is timed to come on outside the heating is on.
 

Similar plumbing topics

R
  • Question
No it won't be why the boiler is on all day...
2 3
Replies
66
Views
5K
  • Question
ok thank you
Replies
2
Views
2K
  • Question
If I understand you correctly, you have...
Replies
3
Views
2K
  • Question
Yes you can. G3 is only with regards to the...
Replies
1
Views
779
  • Question
I'm a bit late but this is how I 'balance' a...
Replies
12
Views
3K