simonhick
Hi,
I have a boiler that is driving me mad.
The boiler in question is a Alpha CD28c lpg. It is in a rented property and has not been used for a long while, although the boiler is only 3 years old.
I have had to change the lpg rig as not to current standards. Initially the boiler would not light at all. I changed the gas valve it now works on hot water no problem but on heating it runs for 30 seconds but no heat to the rads. No lock out or faults neons. Pump runs but get really hot, fan ok. It appears that water not leaving boiler into heating circuit. return hotter.
Alpha mentioned a blockage in boiler. I have completely stripped down boiler and drained system. Both clear and clean.
The boiler runs fine in service mode (rads get hot) as i used this to set up the gas valve with my gas flue analyser.
As soon as back to heating no heating? 240v at diverter valve motor ( does this send 240v back to pcb when switched)
The diverter valve body with valve and seating is clear and heat circulates with motor removed.
I am thinking of changing the diverter valve motor, but worried I have missed something?
Any advise would be appreciated as i am now sick of this boiler and spent alot of time at clients, I thought I had it with the change of the gas valve then this.
cheers
I have a boiler that is driving me mad.
The boiler in question is a Alpha CD28c lpg. It is in a rented property and has not been used for a long while, although the boiler is only 3 years old.
I have had to change the lpg rig as not to current standards. Initially the boiler would not light at all. I changed the gas valve it now works on hot water no problem but on heating it runs for 30 seconds but no heat to the rads. No lock out or faults neons. Pump runs but get really hot, fan ok. It appears that water not leaving boiler into heating circuit. return hotter.
Alpha mentioned a blockage in boiler. I have completely stripped down boiler and drained system. Both clear and clean.
The boiler runs fine in service mode (rads get hot) as i used this to set up the gas valve with my gas flue analyser.
As soon as back to heating no heating? 240v at diverter valve motor ( does this send 240v back to pcb when switched)
The diverter valve body with valve and seating is clear and heat circulates with motor removed.
I am thinking of changing the diverter valve motor, but worried I have missed something?
Any advise would be appreciated as i am now sick of this boiler and spent alot of time at clients, I thought I had it with the change of the gas valve then this.
cheers