Hi,
I am a sparky. I had to check the wiring of a vented system for a landlord who thought the programmer was faulty in one of his properties.
I found, after looking at the wiring diagram for a Y plan, that the system did not have a room stat fitted - just a link wire. The sytem has TRVs on the radiators throughout. I removed the head of the mid-position valve and found it had stuck fast and would not budge.
Can anybody tell me what the disadvantages are of having no room stat? I thought systems had to have boiler interlock in place to save fuel etc.
As the landlord will have to get the valve replaced would there be a good chance that it will last less time than in a system fitted with a room stat?
Cheers.