Hi guys got a fault thats puzzling me, Had call to repair a 9 year old ariston microgenius 23 thats running on LPG, Sorted the initial fault of no ignition by changing the fan, However while watching the boiler fire up, maybe 3 times out of 5 only the right hand side of the burner ignites and then the left hand side follows about a second or two later, sometimes the left hand side does not ignite and the flame detection knocks it off and goes through cycle again. when i stripped out the burner found it to be only about 14 months old and looked like new, no sign of blockages and i stripped out the 12 nozzles and checked them all, also no blockages, inlet pressure was a constant 35 mb on DHW and CH, on burner side, 18mb on CH and 32 mb on DHW, another thing i noticed was what sounded like pulsing on fire up but my u gauge was not moving, Forgot to say i also re set the soft start to check that was not the problem but still no change,
Any help would be greatly appreciated.