Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Boiler overheating High Temps in the Boilers area at Plumbers Forums

Status
Not open for further replies.
Yes to bump it upto 7kw

Or to live with it, which isn't the best option
You seem like an expert. Auto bypass, pipe thermostat, mixer valve all these potential repair options that have been advised by different users/ plumbers will any of these not do the job? What’s the worst that can happen if I left it as it is? Baxi have changed the thermostat and the issue of boiler overheating and switching off has not been apparent lately. Will I need to change thermostat every couple of years on the boiler?
 
Auto bypass will help,

Pipe thermostat won't do bugger all
Same with a blending valve

And will put undue wear on the boiler but shouldn't harm it that much
 
Auto bypass will help,

Pipe thermostat won't do bugger all
Same with a blending valve

And will put undue wear on the boiler but shouldn't harm it that much
I shall look at the radiator option for now. Thankyou so much for all your informative advise. It’s truly really appreciated.
 
More than welcome
 
hi mossy , if this is the heat only boiler it has no pump overrun , you can get a kit to sort this problem , a delayed timer .
 
hi mossy , if this is the heat only boiler it has no pump overrun , you can get a kit to sort this problem , a delayed timer .

How's that going to sort the heat capacity issue ??
 
it won't , just looking to get some heat away from the boiler ,looks like a simpler solution than adding a big rad .
 
Status
Not open for further replies.

Similar plumbing topics

You will need a check valve to stop reverse...
2 3
Replies
61
Views
7K
well, I really cannot see what extra features...
Replies
10
Views
1K
IMO, the boiler should be derated to ~ 20kw...
Replies
18
Views
919
Thanks will try this out, appreciate the help
2
Replies
47
Views
5K
Set the ufh mixer to 30-40 / what the design...
Replies
1
Views
2K
Back
Top