Hi Guys,
Need some help. I have calculated online the BTUs for the rads (calculator used T65) then when purchasing I was looking at the T65 radiator calculations.....
But I have since noticed, Europe uses T50 as standard. What calculation would I use to convert the T65 BTU needed to the new T50 (I presume I would need to increase the number).

Or would it stay the same and I would just need to choose rad BTU's at T50?
 
Flow plus return temp

Divide by two

Minus your room temp

Eg

65+50

115/2

57.5

Mins let’s say 18

Gives you a delta t of 39.5

Delta t of 50 you would need your flow and return around 75-65

Which if you have a condensing boiler is bad

TBH I would work off a delta t of 40
 
Hi Guys,
Need some help. I have calculated online the BTUs for the rads (calculator used T65) then when purchasing I was looking at the T65 radiator calculations...
But I have since noticed, Europe uses T50 as standard. What calculation would I use to convert the T65 BTU needed to the new T50 (I presume I would need to increase the number).

Or would it stay the same and I would just need to choose rad BTU's at T50?
Output of a 50 deg rad is (50/60)^1.3. I , can't work this out in my present location but very easily done on a spreadsheet . You can also and easier look it up in a radiator temperature correction table.
 
Hi Guys,
Need some help. I have calculated online the BTUs for the rads (calculator used T65) then when purchasing I was looking at the T65 radiator calculations...
But I have since noticed, Europe uses T50 as standard. What calculation would I use to convert the T65 BTU needed to the new T50 (I presume I would need to increase the number).

Or would it stay the same and I would just need to choose rad BTU's at T50?

Slightly misread your post so if the calculation was based @ T65 then the correction factor to run @T50 is 1.41, (65/50)^1.3.
IF it had been based @T60 then the correction factor to run @T50 is 1.27, (60/50)^1.3.
 

Similar plumbing topics

Standard temps for full temp heating systems...
Replies
12
Views
6K
Don't know about the legalities but seems to...
2 3 4 5
Replies
106
Views
12K
  • Question
Replace the old radiators larger rooms need 2...
Replies
2
Views
1K
Replies
17
Views
2K
Back
Top