I suppose they couldn't do the heat loss calcs so then couldn't recommend the correct output rad.
If you are wondering how the correction factors that Siricosm quoted then they are (obviously) based on a T50 rad or sometimes called a 50 deg rad, this is based on the rad flow and return temps and the required room temp which is often assumed at 20C, the "deg rad" is then the mean rad temp-the required room temp, if you had flow/return temps of 75/65 and a required room temp of 20 then you would have a ((75+65)/2)-20, a
50 deg (or T50) rad, you can see from the table below that a 40 deg rad will give ~ 75% output of a 50 deg rad so the correction factor is 1/0.748 or 1.34 and so on. the output is the ("deg rad"/50)^1.3. You probably know this anyhow but no harm to show that rads have to be very oversized if using very low flow temps like with Heat Pumps.
Flow temp | 75 | 65 | 55 | 45 |
Ret temp | 65 | 55 | 45 | 35 |
Mean temp | 70 | 60 | 50 | 40 |
"deg rad" | 50 | 40 | 30 | 20 |
Output | 100.0% | 74.8% | 51.5% | 30.4% |
X Factor | 1.00 | 1.34 | 1.94 | 3.29 |