As far as I am aware the 3200 controller doesn't have weather comp built in as standard although they will almost definitely have a module you can add to activate it. I've not seen any option for weather comp curves whilst setting up.
The smaller P1 and P4s use a modulating pump controlled by the controller to control the pump speed to maintain the return temperature to the required temp. This may be what is on the drawing.
On the last quote we got a couple of weeks ago they added an export pack which was not on the quote before. I queried what it was (listed as CB mixer) thinking they'd specced two variants for the shunt pump as I couldn't understand how they could spec a pump without asking for hydraulic spec of system.
If they had said it was weather compensated mixing it would have made sense but they didn't, they simply said it was an export pump and mixing valve set. I've a feeling this has all only recently come about.
Yes providing the boiler is sized correctly.
If you could control the flow to buffer depending on flow rate as opposed to temperature, it would make more sense.
In the 2 port configuration, with heating on in depths of winter and customer runs a bath or has a long shower. Buffer temp will drop fairly quickly, heating pump will be on so flow to buffer will be reversed, how's the buffer going to remain charged?
The buffer works when the boiler isn't even awake.
Demand established :-
Buffer satisfies load whilst boiler gets to 55c and flue up to 100c
Boiler hits :- 55c and flue 100c 3 port and pump wind in ..... Buffer still providing load satisfaction
Boiler hot and 3 port swings in:-
Buffer almost depleted but boiler coming on line.
Load side pumps pull from easiest route which is boiler now that the 3 way is playing ball.