Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Buffer Tanks - 2 or 4 port connections in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.
The original tender design was done by consultants in London and a spec produced for pricing. Wilmot Dixon won the contract on that spec. When the contract was signed, the consultants pulled the design and said WD had to use their own design to which they just rebadged the original with out checking to see if it will do the job, so the responsibility lies with them. Hence the QS sat with his head in his hands when we said it won't work. No one had told him why, the just refused to price the job.

So, if the job was tendered on a design, the design was pulled and they had to do it themselves (which presumably wasn't included in the original spec)..... let's see, redesign from the original, V.Os/AIs, I'm sure somebody looking at it on the contractual side could make a very good case for ££££££ of extras! :grin:
 
Possibly, but I think now the system has been commissioned, the council will not accept any AI's or variation orders for major system and plant alterations. WD will lose out big time.
 
had an email today from Wilmot Dixons QS basically saying to give them a list of what our demands are to take the installation on and give them a price for it. They are getting desperate as the council want to take ownership of the system to claim RHI but WD cant fulfil their contract without having an O&M agreement in place. could be ££££££'s for us and a good 1st step for our new business venture.
 
Basically, a complete redesign incorporating the existing plant plus whatever extra is needed to get it working correctly. At least an additional boiler, pump sizes?, incoming gas large enough? etc. etc.
Merry Xmas!! :clap:
 
exactly, we need to redo all the calculations to check everything will work, the hydraulics are ok. dont think we'll put another boiler in but will get the council to accept that a 200kw boiler is not gonna cover 70% of a 1.4mw of peak demand. although the biomass will be running flat out and they will get the full rhi, they have to realise its a token boiler and a tick in the renewables box but thats about it and the gas boilers will be doing most of the work.
 
How and when are the gas boilers controlled to kick in? Is it through the buffer temperatures?
 
the gas boilers will kick in either if the biomass goes into fault or when the biomass is running at full power and the return temperature drops below 65 degrees.
 
Status
Not open for further replies.

Similar plumbing topics

  • Question
Plate load it then and use the 500l cylinder...
Replies
9
Views
2K
  • Question
No as the temp wouldn’t get as hot as the...
Replies
1
Views
1K
Working at a flow temp of 30 ? As a dt of 30...
Replies
6
Views
4K
200% won’t be the reason the cylinder isn’t...
Replies
10
Views
1K
Behind the control panel the cylinder unit...
Replies
7
Views
1K
Back
Top