And we have all seen proper filling loops with one tap onIt was my understanding that you required two taps by regs anyway?
You can see why you have the NRV on the cold, as it's less of a dead leg.
Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws
Discuss Has my builder ruined my boiler? in the Boilers area at Plumbers Forums
And we have all seen proper filling loops with one tap onIt was my understanding that you required two taps by regs anyway?
You can see why you have the NRV on the cold, as it's less of a dead leg.
Should be. But how many customers actually remove it though.But there’s no dead leg because the hose should be removed
I wasn't disputing the fact that the hose shouldn't be removed, I was just simply stating that hardly anyone actually removes the link.No but I’m arguing regs if you say there should be two taps then the hose should also be removed. Sorry I’m not being pedantic I’m genuinely querying. I cannot see what difference it makes what the reasoning is for the nrv on cold
You're right, there isn't one when the hose has been removed. But my point kind of was, no one ever removes the hose.Oh I totally agree with two taps don’t get me wrong but to me it’s logical to stop the heat at the return end so there is no inadvertent heating of the cold side. I cannot see where a dead leg occurs if there is no hose though.
Sorry to sound blunt but your title is immediately accusatory. If in fact it was a builder or a plumber that worked on the boiler and not a gas safe engineer then I’m afraid the fault lies with you
Thanks Riley, the only problem I now have is, the extension build is new and I have not signed off on the builder's snagging list. So a small final payment is due. I don't know whether I should trust him to put it right or to call in a known good plumber to rectify his work.
Didn’t say to fit a zone valve did I. OP alluded to the rebuild of the boiler which I was questionningWhy do you need to be gas safe to fit a zone valve?
As you say however you are well within your rights also to refuse access if you feel they have acted outside scope or unlawfullyLegally the original contractor is entitled to be given reasonable opportunity to put the situation right. You’re well within your rights to insist the work is undertaken by a competent person. Sounds very like you have the experience to decide for yourself if the guy is flanneling you.
Didn’t say to fit a zone valve did I. OP alluded to the rebuild of the boiler which I was questionning
As you say however you are well within your rights also to refuse access if you feel they have acted outside scope or unlawfully
Don't blame you for keeping it. I'm keeping my Glow Worm Ultimate going for as long as I can.
We've taken condensing boilers out which have been 6/7 years old which were beyond repairing. Admittedly these were probably ones that haven't been well maintained or fitted well.
My Ideal Mexico is of 1997 vintage
On a sep note, efficiency ratings as specified by all manufacturers are ONLY seen by a VERY small number of UK home owners.
Why?
The efficiencies are calculated at a flow temp of 50 degrees C and a return of 30 degs C. However, most UK home owners would claim the system is faulty at such low flow temps so new (efficient boilers) are commissioned to run at a flow of 70 & (at best) a return of 50. This delivers just a few % of potential and rarely (if ever) pays back the investment.
How do you achieve that then?
Increase the resonance time/reduce flow rate through radiators?
Surprising in this day and age of smart TRVs there not measuring flow/return temp.
The temperature differential across the radiator.Achieve what?
Flow rate. Slower the flow rate higher the temp drop.The temperature differential across the radiator.
The emphasis being "plumber" or heating engineer !If I accept what you are saying and I bow to your superior knowledge. I don't need to call the builder back. I just need a competent Gas Safe plumber to investigate and fix the problem? Know any good and qualified trustworthy central heating engineers in the North West London area?
The emphasis being "plumber" or heating engineer !
If the cold water feed to the filler loop is boiler side of the new valves you should be able to pressurise the system. It's unclear what's where from the pictures. It needs a sketch of the pipework with valve positions. If you turn a tap into you get hot water? Too much guesswork without a diagram.