Heating Bangs when switching off. | Plumbing Jobs | The Job-board | Page 2 | Plumbers Forums

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

American Visitor?

Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Heating Bangs when switching off. in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.
Great help guys thanks very much. One more question where should I fit the bypass valve. Close to the boiler or in the airing cupboard.

Cheers.
 
They were hissing air when the system was refilling so guess they are air vents.

Airing cupboard

I would fit it in between the port valve tees and straight onto the return
 
Airing cupboard

I would fit it in between the port valve tees and straight onto the return
Yes it needs a bypass.
If you try holding the valve open whils someone turns heating off you’ll see if it stops the bang
Wouldn’t the rad in the hall and heated towel rail act as a bypass. Neither of these have trv’s.
So removing that landing rad shouldn’t have made a difference. He also joined the pipes from the rad he removed and it was still banging.
 
Wouldn’t the rad in the hall and heated towel rail act as a bypass. Neither of these have trv’s.
So removing that landing rad shouldn’t have made a difference. He also joined the pipes from the rad he removed and it was still banging.

If these are piped in before any port valves yes they would
 
Wouldn’t the rad in the hall and heated towel rail act as a bypass. Neither of these have trv’s.
So removing that landing rad shouldn’t have made a difference. He also joined the pipes from the rad he removed and it was still banging.


Not if they’re after the valve and they most likely are.
The bypass needs to be before the valve for when the valve shuts!
 
Not if they’re after the valve and they most likely are.
The bypass needs to be before the valve for when the valve shuts!


Hi

I had a plumber attend yesterday and the valve was faulty, when taken off you could hear it making a grinding noise. He replaced the valve and the banging stopped but did say it probably needs a bypass valve fitting between the pump and valves then into the return. After a few hours the banging returned but it was much quieter. The plumber said the new valve is much stronger than the old one.

The bypass is being fitted Thursday so I will let you know what happens.

Cheers for all your advice.

Regards.

Paul.
 
Hi Paul
I would suggest that you check that the zone valves are actually positioned correctly for the differential pressure being created by the pump. The type of sound you have described indicates to me that a zone valve is slamming back when closing - this happens when a valve is positioned the wrong way to the flow - but looking at the photo they seem good to me but obviously I cant see the whole system layout design - so its difficult to be sure whats going on?
Best of luck getting it sorted... Bill
 
Hi All,

I had the bypass fitted but there is still a slight bang when turning off. It still pushes water into the header tank as well. I also had fitted a new pump as the old one was nearly blocked. I have fitted a magnaclean on the return to the boiler and you wouldn't believe what muck came out of it in 24 hours.

Should I just put the radiator back.

Cheers.
 
I would drain down and wack some x800 in the system for a week then drain it down again and fresh inhb
 
I already did flush and the water ran clean. I opened all the bleed valves to get all the water out. The pump was old, dated year 2000 so it needed replacing anyway.
 
Just updating again on this. I refitted the radiator and now the heating Bangs even more. Really am at a loss. Anybody with any further ideas.
 
The fact that you have water flowing out the vent pipe when the system shuts down indicates you still have a fault, probably a blockage somewhere near the expansion pipe. You could try turning the speed on the pump down to its minimum to see if the noise reduces. Another thing to try would be to remove the rad again, empty it, refit, turn on the valves but don't bleed it. (it should act as an expansion vessel).
One thing i noticed looking at the pictures is the vent from the boiler looks like its running horizontal along the ceiling, so it may be possible that the system has an air lock.
 
Forgot to say, that as you mentioned the amount of muck in the magnet suggests that the system needs a good clean.
 
Forgot to say, that as you mentioned the amount of muck in the magnet suggests that the system needs a good clean.
Thanks for your advice. The pipe or pipes running across the garage ceiling are the flow and return to the boiler. The vent pipe is in the airing cupboard and goes about 18 inches abouve the header tank in the loft. When filling the heating back up after draining it doesn't bang, it's only when all the air is out the system so similar to your radiator test. Turning the pump down reduced the bang noise.

Cheers.

Paul.
 
Got a picture of the new by-pass that’s been fitted ? Hard to tell from airing cupboard picture but is the open vent an cold feed teeing in just before pump
 
Got a picture of the new by-pass that’s been fitted ? Hard to tell from airing cupboard picture but is the open vent an cold feed teeing in just before pump

IMG_3230.JPG


IMG_3231.JPG
 
Where's the bypass valve all I see is a full bore ISO valve ?
 
The valve put in on the by-pass looks like a ball fix turned 1/3 off have you tried opening this fully an seeing if this stops the banging
*shaun beat me to it,but that isn’t correct for a by-pass that’s why you still have the banging
 
The plumber said it didn't need one, I thought it might and I asked again whether it needed to be 22mm. I can change it myself if you are able to advise what to get and where to put it. If the valve is fully open then yes it does stop it banging.

One question, I have lived in the house for 13 years without a single bang. Why would this start after removing the radiator.
 
The valve put in on the by-pass looks like a ball fix turned 1/3 off have you tried opening this fully an seeing if this stops the banging
*shaun beat me to it,but that isn’t correct for a by-pass that’s why you still have the banging



The plumber said it didn't need one, I thought it might and I asked again whether it needed to be 22mm. I can change it myself if you are able to advise what to get and where to put it. If the valve is fully open then yes it does stop it banging.

One question, I have lived in the house for 13 years without a single bang. Why would this start after removing the radiator.
 
I didn’t even pick up on that it was 15mm,that won’t help an then with the type of valve that will neither. You’ve said that with it fully open the banging stops.I could only say that since the 13years you’ve been there that the pipework /heatexchanger has become restricted.
 
I didn’t even pick up on that it was 15mm,that won’t help an then with the type of valve that will neither. You’ve said that with it fully open the banging stops.I could only say that since the 13years you’ve been there that the pipework /heatexchanger has become restricted.

Cheers for your help. Could you tell me what valve I need and where it should go.
I assume the valve is operated by bar pressure
 
Status
Not open for further replies.

Similar plumbing topics

C
I’m not posting here to agree to do/looking...
Replies
1
Views
812
If you are paranoid, refill, circulate and...
Replies
2
Views
315
As part of deep house renovation, planning to...
Replies
0
Views
879
  • Question
It’s expansion and contraction do you have the...
Replies
1
Views
531
Back
Top