bypass valve open vented system - Google pretraga ask your plumber who installed your by-pass to come back an rectify
Your a star cheers. Is it in the right place above the valves
We recommend uHeat for Underfloor Heating Systems, and The Wetroom Store for all things bathrooms and wetrooms. They provide discounts for forum members.
Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws
bypass valve open vented system - Google pretraga ask your plumber who installed your by-pass to come back an rectify
Has a Plumber put that in?
Has a Plumber put that in?
It will do there if it is 22mm and automatic. I am presuming you have a 3 mtr min loop from boiler and back to boiler via by-pass?
View attachment 31830
One question, I have lived in the house for 13 years without a single bang. Why would this start after removing the radiator.
The distance from the boiler to the by pass is about ten meters. I will change the size of the plumbing and use solder joints as it looks a bit messy. I can fit it somewhere else if it works better. I would rather it be correct. Wish I had done the work myself.
Does the pressure have to be regulated by the pump flow speed. Cheers.
Does the pressure have to be regulated by the pump flow speed. Cheers.
Pump is on 2 as the system is quite large 12 rads.What speed is the pump on now?
Pump is on 2 as the system is quite large 12 rads.
Cheers.
I
If it works well it's fine. You want them on the lowest setting that works and gives the right flow and return temps.
With the valve:-
screw it shut, turn on the heating and hot water so both Motorised valves are open and the pipes start to get hot. Slowly open the Auto by-pass 1/4 turn at a time, (a few seconds in between turning), until you feel hot water flow through the by-pass. Then close it back around a half turn.
That's the best explanation I can give on a Forum. I would be going to greater lengths to set things up and balance the system if I were doing this in person but it will do!
Please do come back and tell us how you went on.Thanks I'll do it on Saturday and let you know how it goes.
Cheers.
Hi.Please do come back and tell us how you went on.
Does the light on the pump flash or stay solid?
Okay. That's fine. If you were running it in flashing mode, then it would not be running fixed-speed, and the automatic bypass valve wouldn't be able to work as it should.
When you say restrict the flow on hot water,is this when the system is running eg demand from heating/hot water? The hot water coil should have a balancing valve on it that should be restricted (which from the pic you have one after the 2port) to stop the heat just whizzing around the coil and giving less to heating
It should be restricted yes,but are you only getting flow through the by-pass valve when there is still demand for ch or hot water an your closing the balancing valve?