The size of the room is relevant in relation to temperature lift of course but it lifts the temp fine in the barn when there is no demand from the bedrooms run through the 9 port manifold as the boiler doesn’t drop temperature.
I have already asked for a second opinion from aanother ufh engineer (in addition to the original installer) which is when I had received my conflicting diagnosis (one said the LLH is required, other said route cause of issue is diameter of feed piles from boiler to manifold(s) due to the long runs of pipe - hence my post on here.
Either solution ref above is a fairly major job by the looks of things and I am concerned that one or the other proposed solution (or worse still both!) will not resolve the issue of the boiler temperature plummeting like a stone due to demand
I have already asked for a second opinion from aanother ufh engineer (in addition to the original installer) which is when I had received my conflicting diagnosis (one said the LLH is required, other said route cause of issue is diameter of feed piles from boiler to manifold(s) due to the long runs of pipe - hence my post on here.
Either solution ref above is a fairly major job by the looks of things and I am concerned that one or the other proposed solution (or worse still both!) will not resolve the issue of the boiler temperature plummeting like a stone due to demand